I need help hooking up a new Nest thermostat to an old millivolt floor furnace by using a 24v step-down transformer. The model of the floor furnace is: Kresky Gravity Floor Furnace 46 F,D . My current (old) thermostat says "LUXPRO" on the front panel. On the back of the panel, on the inside, it says:
S.P.S.T
T101141 / PSM30
Heat Only
0.15 to 1.2 Amps
Max 30 Volts A.C.
I am upgrading to a Nest thermostat, and have two wires in my wall: Rh and W.
Before ordering the Nest, I emailed Nest support to check compatibility and attached a photo of my wiring. Their response was:
Congratulations! Based on your picture it does appear that your system is compatible with the Nest Learning Thermostat! It appears that you a conventional heating only system. The red and white wires coming through from the back of the thermostat are what will need to be connected to Nest. The red wire will be connected to the Rh terminal for power and the white wire will connect to the W1 terminal for heating.
Unfortunately neither they nor I realized that I had an ancient millivolt system that was actually incompatible with Nest (I figured it out when I traced the thermostat wiring after a power outage a few days ago). FYI: I have what appears to be two insulated wires, and not a single copper one, it's my understanding that the millivolt power is coming from a thermopile (vs. a thermocouple).[1]
Not yet giving up hope, I called Nest support and asked if there were any workarounds. The support technician told me he'd heard some customers had success with using 24v step down transformers in tandem with their existing millivolt system. With this knowledge in hand, I set out to research. So far, I've found three useful threads about using 24v transformers in this kind of situation:
radiothermostat.com • View topic - Powering / Wiring "C" on a 2-Wire, Milliamp System
radiothermostat.com • View topic - Wiring a two wire boiler system
Powering A 24v/millivolt Thermostat To Control A Gas Stove ? - HVAC - Contractor Talk
All of the above threads suggest that the wiring goes something like this:
W from furnace (common, -0.7VDC ?) --> W on T-Stat
24 VAC power from transformer (+/- ?) --> C on T-Stat
R from furnace (+0.7VDC ?) --> RH on T-Stat
24VAC power from transformer (+/- ?) --> RH on T-Stat
As you can see, I'm still a bit fuzzy...
•Which of the 24v wires (+/-) goes to which terminal (C, Rh)?
• Is it really okay that the 0.7VDC furnace/millivolt Rh wire and one of the 24VAC transformer wires will be on the same Rh connector on the Nest? If I understand correctly, the reason it doesn't matter that I'll have two wires on the Rh connector is because they are part of two different circuits--is that right?
Regardless, I will want to check with a multimeter to make sure the voltage coming into the Nest is within 20.5 and 27.5, since those are the min/max it will accept according to this page: Nest | Heating and cooling systems that are inc...
Anyway, please let me know if I understanding any of this incorrectly.
Last but not least, here are some of the step down transformers I found. Would any of them work?
Functional Devices Inc / Rib TR50VA005 Transformer, Control, Input 120, Output 24
Honeywell AT72D1683 Step-down Transformer 24 Volt
Amazon.com: Honeywell AT150A1007 Transformer, 120/208/240 volt, with universal mount, foot, plate or knockout.: Home Improvement
Amazon.com: Transformer: Home Improvement
AT140A1000 - Honeywell AT140A1000 - Foot Mounted, Plate Mounted, Clamp mounted or Panel Mounted 120 Vac Transformer (40VA)
Thanks in advance! I apologize that this is so long, but I wanted to be as specific as possible.
[1] Are kresky furnace repair parts available I have gravity - JustAnswer
S.P.S.T
T101141 / PSM30
Heat Only
0.15 to 1.2 Amps
Max 30 Volts A.C.
I am upgrading to a Nest thermostat, and have two wires in my wall: Rh and W.
Before ordering the Nest, I emailed Nest support to check compatibility and attached a photo of my wiring. Their response was:
Congratulations! Based on your picture it does appear that your system is compatible with the Nest Learning Thermostat! It appears that you a conventional heating only system. The red and white wires coming through from the back of the thermostat are what will need to be connected to Nest. The red wire will be connected to the Rh terminal for power and the white wire will connect to the W1 terminal for heating.
Unfortunately neither they nor I realized that I had an ancient millivolt system that was actually incompatible with Nest (I figured it out when I traced the thermostat wiring after a power outage a few days ago). FYI: I have what appears to be two insulated wires, and not a single copper one, it's my understanding that the millivolt power is coming from a thermopile (vs. a thermocouple).[1]
Not yet giving up hope, I called Nest support and asked if there were any workarounds. The support technician told me he'd heard some customers had success with using 24v step down transformers in tandem with their existing millivolt system. With this knowledge in hand, I set out to research. So far, I've found three useful threads about using 24v transformers in this kind of situation:
radiothermostat.com • View topic - Powering / Wiring "C" on a 2-Wire, Milliamp System
radiothermostat.com • View topic - Wiring a two wire boiler system
Powering A 24v/millivolt Thermostat To Control A Gas Stove ? - HVAC - Contractor Talk
All of the above threads suggest that the wiring goes something like this:
W from furnace (common, -0.7VDC ?) --> W on T-Stat
24 VAC power from transformer (+/- ?) --> C on T-Stat
R from furnace (+0.7VDC ?) --> RH on T-Stat
24VAC power from transformer (+/- ?) --> RH on T-Stat
As you can see, I'm still a bit fuzzy...
•Which of the 24v wires (+/-) goes to which terminal (C, Rh)?
• Is it really okay that the 0.7VDC furnace/millivolt Rh wire and one of the 24VAC transformer wires will be on the same Rh connector on the Nest? If I understand correctly, the reason it doesn't matter that I'll have two wires on the Rh connector is because they are part of two different circuits--is that right?
Regardless, I will want to check with a multimeter to make sure the voltage coming into the Nest is within 20.5 and 27.5, since those are the min/max it will accept according to this page: Nest | Heating and cooling systems that are inc...
Anyway, please let me know if I understanding any of this incorrectly.
Last but not least, here are some of the step down transformers I found. Would any of them work?
Functional Devices Inc / Rib TR50VA005 Transformer, Control, Input 120, Output 24
Honeywell AT72D1683 Step-down Transformer 24 Volt
Amazon.com: Honeywell AT150A1007 Transformer, 120/208/240 volt, with universal mount, foot, plate or knockout.: Home Improvement
Amazon.com: Transformer: Home Improvement
AT140A1000 - Honeywell AT140A1000 - Foot Mounted, Plate Mounted, Clamp mounted or Panel Mounted 120 Vac Transformer (40VA)
Thanks in advance! I apologize that this is so long, but I wanted to be as specific as possible.
[1] Are kresky furnace repair parts available I have gravity - JustAnswer
#2
Question about the Nest thermostat? Does it use batteries? If so you should simply be able to install the Red wire to RH and the white wire to W. Otherwise you will need a 24V transformer and a spst relay (24VAC coil).
#3
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hi hvactechfw. It does have a built-in battery, but it needs to get recharged off the C wire, so I will need the 24v transformer. Why do I need a "spst relay (24VAC coil)"? Will it not work if I just wire the 24v transformer wires to C and Rh?
Thanks for your help!
Thanks for your help!
#4
IF you have a milivolt system then you can not do that! When Rh and W are shorted that connects the milivoltage produced by the thermopile is transferred from the Rh wire to the W wire which connects to the gas valve completing the circuit. If you were to interject 24VAC on the Rh terminal you could ruin the gas valve. A milivolt system is a DC system which uses less that 1VDC. Are you sure you have a Milivolt system? It very well could be that you have a 24V heating only 2 wire system which is not a milivolt system.
#5
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wow, thank you very much for explaining that. In that case, can you tell me more about the spst relay (24VAC coil)? How does that work/where does it belong in the wiring diagram? Thank you again! I've done a lot of internet research and asked this question to multiple people and no one has known the answer except you.
Edit: Yes, I am sure that it's a millivolt system. I traced the wires all the way to the furnace, and they end at what I assume is the thermopile (the wires go into a small box next to the pilot light). The furnace has no other electrical wiring on it or near it, so it must be millivolt.
Edit: Yes, I am sure that it's a millivolt system. I traced the wires all the way to the furnace, and they end at what I assume is the thermopile (the wires go into a small box next to the pilot light). The furnace has no other electrical wiring on it or near it, so it must be millivolt.
#6
DO you have a millivolt system? That is the first thing you need to be sure of. I also do not understand how Nest said that your system would work when you need at least 3 wires to the thermostat for it to operate (you said you need to connect C) so you would need wires on Rh, W, and C. do you have the ability to run 3 wires to the stat? Do you have an extra wire in the loom already there and not being used?
#7
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nest is compatible with 2 wire 24v systems that have only Rh and W and Nest Support thought that's what I had (and also what *I* thought I had) until A) We had a power outage, and the thermostat continued to work and B) I traced the wires from the thermostat all the way to the furnace, and noticed that they end at a small box right next to the pilot light. And there is no other wiring running into or out of the furnace.
As for my existing wiring—currently there are only the two millivolt Rh and W wires running to the stat, but I do have the ability to easily run as many extra wires to the stat as needed, so that's not an issue. The wiring is very accessible.
As for my existing wiring—currently there are only the two millivolt Rh and W wires running to the stat, but I do have the ability to easily run as many extra wires to the stat as needed, so that's not an issue. The wiring is very accessible.
#8
Can you provide me with a link to a installation manual. The pdf file on the Nest website is corrupted. You implied that nest is compatible with 2 wire systems. If you must provide 24V to the thermostat then that is not possible with only 2 wires as then you are left with no signal wire back to the furnace. HOW DO YOU KNOW YOU HAVE A MILLIVOLT SYSTEM?
#9
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nest is "compatible" with 2 wire 24v systems because it can charge itself using the AC supply for the heat signal while the heat is on. It then utilizes its battery until the heat is on again, at which point it again charges itself during the time the room/building is being heated.[1] How well that actually works in practice is another question, but it IS supported by Nest, and you can verify this by using their compatibility checker.
As for how I know I have a millivolt system... there are two reasons:
1) We had a power outage, and the thermostat continued to work, even though literally *nothing* else had power, and there is no battery backup in the existing thermostat.
2) I traced the wires from the thermostat all the way to the furnace, and noticed that they end at a small box right next to the pilot light. There is no other wiring running into or out of the furnace.
[1] Undocumented Nest incompatibility with single-stage wiring
As for how I know I have a millivolt system... there are two reasons:
1) We had a power outage, and the thermostat continued to work, even though literally *nothing* else had power, and there is no battery backup in the existing thermostat.
2) I traced the wires from the thermostat all the way to the furnace, and noticed that they end at a small box right next to the pilot light. There is no other wiring running into or out of the furnace.
[1] Undocumented Nest incompatibility with single-stage wiring
#10
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here is the link to the Nest install guide.
Edit: I just downloaded it and opened it. It is not corrupt.
Edit: I just downloaded it and opened it. It is not corrupt.
#11
for some reason I can not download it. Check for a PM from me. By the link you gave for the incompatibility with single stage wiring, that is exactly what I was thinking and that you will need to have 3 wires to the stat for reliable operation. I will draw you up a schematic.
#13
Emily Atlas
voted this post useful.
#14
Member
Join Date: Jun 2011
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I looks like you have your answer on the wiring. I work FT as a Home Energy Rater and Auditor. I installed my new Nest about 10 days ago.
My question is not about the wiring, but why you are not replacing your extremely old and wasteful floor furnace with something much more effective and safe a few bucks at the same time?
John Nicholas
My question is not about the wiring, but why you are not replacing your extremely old and wasteful floor furnace with something much more effective and safe a few bucks at the same time?
John Nicholas
#15
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Unfortunately we are in an apartment, so we can't make those types of upgrades. I can only do this upgrade because it's very simple, and all it's going to take in terms of alterations to the building is two screws inside my closet to mount the transformer. One of the reasons we specifically want the Nest is for safety re: the floor furnace. The Nest has motion sensors/auto away functionality and ability to remote control via iPhone app. This is important because about a week ago, the dog dropped a tennis ball on the floor furnace while we were watching a movie, and the whole room filled with smoke before we noticed. We managed to catch it since we were home, but it'd be great to have the thermostat shut off the heat automatically if we forget to do so, and also great to have the ability to shut it off even faster via the iPhone app (e.g. if we remember that we forgot to turn it off when we're half way to our destination).
On a related note, I upgraded our fire alarm to a dual sensor (ionizing/photoelectric) model so that it will better detect smoldering fires.
On a related note, I upgraded our fire alarm to a dual sensor (ionizing/photoelectric) model so that it will better detect smoldering fires.
#16
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Also, it seems that I may not need that SPST relay after all, as long as the Nest circuitry is properly designed, which can be checked with a multimeter. Here is the explanation from a user named JackFlash at Ask Metafilter (I posted this question there as well):
...
He made a second post on how to check to make sure the circuits are in fact isolated:
It is possible that what you are trying will work, depending on how the thermostat is designed.
The reason is that there are two independent circuits. Remember that current has to flow in a complete circle. Drawing it out on paper may help.
The first circuit connects one terminal of the transformer to RH, through the thermostat, out C and back to the other terminal of the transformer. That provides 24VAC between the RH and C terminals and powers the computer circuitry of the thermostat.
The other circuit is furnace thermopile to RH, through the thermostat heat switch, out the W terminal to the gas valve which is grounded to the other side of the thermopile. This circuit sees only the 750 mV of the thermopile. Since there is no connection between the gas valve/thermopile and both terminals of the transformer, this circuit does not see the 24VAC.
This means that making the connections as you propose should work. Just make sure that the C wire connects only to the thermostat and to the transformer and is not grounded to anything else in the system. Since the 24V is AC and not grounded, it doesn't matter which terminals you connect to RH and C.
As a side note, on a more typical 24VAC system, one terminal of the transformer connects to RH and the other terminal of the transformer connects both to the C terminal and the gas valve through the W terminal. So in this case, 24VAC goes through both circuits. So how does the thermostat computer get power if there is no C wire on a 4-wire system? In this case the power for the computer is generated by the connection between RH and W. This current is the same that would turn on the gas valve, but when the heat switch is open, only a tiny amount of current flows to provide power to the computer, not enough current to activate the gas valve.
Since your 24VAC transformer is only providing a tiny amount of power to the thermostat computer, your transformer is way overkill. Instead of 50 watts you probably only need 1 watt since the transformer is not powering the relays in the furnace, only the computer chip. So you could use a much smaller transformer but the one you selected is okay.
The reason is that there are two independent circuits. Remember that current has to flow in a complete circle. Drawing it out on paper may help.
The first circuit connects one terminal of the transformer to RH, through the thermostat, out C and back to the other terminal of the transformer. That provides 24VAC between the RH and C terminals and powers the computer circuitry of the thermostat.
The other circuit is furnace thermopile to RH, through the thermostat heat switch, out the W terminal to the gas valve which is grounded to the other side of the thermopile. This circuit sees only the 750 mV of the thermopile. Since there is no connection between the gas valve/thermopile and both terminals of the transformer, this circuit does not see the 24VAC.
This means that making the connections as you propose should work. Just make sure that the C wire connects only to the thermostat and to the transformer and is not grounded to anything else in the system. Since the 24V is AC and not grounded, it doesn't matter which terminals you connect to RH and C.
As a side note, on a more typical 24VAC system, one terminal of the transformer connects to RH and the other terminal of the transformer connects both to the C terminal and the gas valve through the W terminal. So in this case, 24VAC goes through both circuits. So how does the thermostat computer get power if there is no C wire on a 4-wire system? In this case the power for the computer is generated by the connection between RH and W. This current is the same that would turn on the gas valve, but when the heat switch is open, only a tiny amount of current flows to provide power to the computer, not enough current to activate the gas valve.
Since your 24VAC transformer is only providing a tiny amount of power to the thermostat computer, your transformer is way overkill. Instead of 50 watts you probably only need 1 watt since the transformer is not powering the relays in the furnace, only the computer chip. So you could use a much smaller transformer but the one you selected is okay.
He made a second post on how to check to make sure the circuits are in fact isolated:
By the way, one way to test this is to first connect the transformer to RH and C. This should provide power to the thermostat computer. Also connect RH to R on the furnace. This provides the thermopile voltage to the heat switch. Do not connect the white wire. This will prevent any possible damage to the gas valve. Then adjust the thermostat to turn on heat which closes the switch on W. You probably will hear a click as the switch closes. Measure the AC voltage between W terminal and the white wire. It should be 0. Then measure the DC voltage between the W terminal and the white wire. It should be about 750 mV DC (assuming the pilot light is on). Next adjust the thermostat to turn off heat. Both AC and DC voltage between W and the white wire should be 0. If so, hook up the white wire and you are good to go.
The SPST relay method will work, but shouldn't be necessary if the thermostat is designed as expected with the W and C terminals isolated.
The SPST relay method will work, but shouldn't be necessary if the thermostat is designed as expected with the W and C terminals isolated.
#17
Member
Join Date: Jan 2012
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
rystic: I'm glad I found your post. Thanks for doing the leg work. I got my Nest thermostats yesterday and didn't realize that my free-standing propane stoves are millivolt systems until I talked to Nest support. He suggested a 24VAC relay, but from what you've posted it looks like a simple adapter will work. I will give that a try and report back.
#18
Member
Join Date: Jan 2012
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
This transformer looks pretty ideal. I can't imagine the Nest takes more than 1.67A, but I've got a message in to support asking about the current requirement. I've bought lots of stuff from BG Micro.
BG Micro 24VAC transformer
BG Micro 24VAC transformer
#19
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Since I wanted to mount this in my closet (where there are no outlets) next to an existing light, I went with this one and mounted it on a standard 4x4 electrical box.
Your solution seems a lot easier though, if you have an outlet nearby.
As far as the current goes, according to the Sparkfun teardown of the Nest, it uses "2.1Wh over 3.7V." So according to the calculator I used, the current should come to 0.58 amps.
Your solution seems a lot easier though, if you have an outlet nearby.
As far as the current goes, according to the Sparkfun teardown of the Nest, it uses "2.1Wh over 3.7V." So according to the calculator I used, the current should come to 0.58 amps.
#20
Member
Join Date: Jan 2012
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
That quote from Sparkfun is the capacity of the battery. It doesn't really tell you how many amps Nest needs. The calculator you linked to doesn't have a field for watt-hours. But I'm sure the transformer you're using will work. Have you hooked everything up yet? Were you successful?
#21
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Whoops, you're right. I misread (thought it said W when it was Wh, and didn't realize Sparkfun was only talking about the battery). Definitely do let me know what Nest says when they get back to you. As for my install–no, it's not finished yet. I'm hoping to have some time later today. I'll post here when I do get it finished though.
#22
Member
Join Date: Jan 2012
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I got the first of my two Nests hooked up. The transformer is connected between Rh and C and the stove is connected between Rh and W. Everything seems to be working great so far. The other transformer is going to have to go in the attic so it will be a little more work. You can't really put two wires into the Nest's terminal so you'll need to splice the wires from the transformer and heater together with one wire that goes to the terminal.
#23
If you really do have a millivolt system you are going to let the smoke out of your gas valve by wiring it without the relay. A millivolt system runs on 750mVDC. When the thermostat calls for heat it connects RH and W. Using your transformer you connect RC and C and from your millivolt system you would connect RH and W. This will only work as long as RH and RC are not internally or externally connected otherwise you need to use a relay. Not all 2 wire systems are millivolt systems. Goodluck with your endeavors.
#24
Member
Join Date: Jan 2012
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If you really do have a millivolt system you are going to let the smoke out of your gas valve by wiring it without the relay.
#25
Member
Thread Starter
Join Date: Jan 2012
Location: USA
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
hvactechfw: By the sound of it, neither I nor SESteve have RC wires, since our systems are heat only (no cooling). We have Rh and C from the transformer, and Rh and W from the millivolt system. Both Rh wires go into the same terminal on the Nest*, and C and W go into their own terminals. The reason this is okay, according to JackFlash at Ask Metafilter, is because:
*Via a pigtail wire splice due to limited space on the Nest terminal.
there are two independent circuits. Remember that current has to flow in a complete circle. Drawing it out on paper may help.
The first circuit connects one terminal of the transformer to RH, through the thermostat, out C and back to the other terminal of the transformer. That provides 24VAC between the RH and C terminals and powers the computer circuitry of the thermostat.
The other circuit is furnace thermopile to RH, through the thermostat heat switch, out the W terminal to the gas valve which is grounded to the other side of the thermopile. This circuit sees only the 750 mV of the thermopile. Since there is no connection between the gas valve/thermopile and both terminals of the transformer, this circuit does not see the 24VAC.
The first circuit connects one terminal of the transformer to RH, through the thermostat, out C and back to the other terminal of the transformer. That provides 24VAC between the RH and C terminals and powers the computer circuitry of the thermostat.
The other circuit is furnace thermopile to RH, through the thermostat heat switch, out the W terminal to the gas valve which is grounded to the other side of the thermopile. This circuit sees only the 750 mV of the thermopile. Since there is no connection between the gas valve/thermopile and both terminals of the transformer, this circuit does not see the 24VAC.
The SPST relay method will work, but shouldn't be necessary if the thermostat is designed as expected with the W and C terminals isolated.
#26
Member
Join Date: Jan 2012
Location: USA
Posts: 7
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I heard back from Nest support. They said "Nest draws between 30mA – 100mA, where 100mA is the optimum amount." That's pretty minimal. The transformer I ended up using supplies up to 1A, so it's plenty for the job.
#28
Member
Join Date: Feb 2012
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
millivolt relay system
I do not feel comfortable without using a relay for isolation.,
I only had a 24VDC relay, which would make a buzzing noise if hooked to AC. So I took a bridge rectifier out of an old power supply and used it to make DC to run the relay. See schematic included:
I got a big 24VAC transformer from eBay. Probably way overkill for this application.
I only had a 24VDC relay, which would make a buzzing noise if hooked to AC. So I took a bridge rectifier out of an old power supply and used it to make DC to run the relay. See schematic included:
I got a big 24VAC transformer from eBay. Probably way overkill for this application.
#29
Member
Join Date: Aug 2012
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sorry for ressurecting an old thread but it fits in with powering a Nest. I've got a Goodman Heat / AC unit - it is about 13 years old - nothing fancy about it. Nest wiring adviser says I should have no problem with my standard R, Y, W, G wiring. I've read the problems about the Nest not getting enough power and ideally a C wire would solve any potential problems. From what I can see and find - I'm not sure where or how to get the C wire off of my control board of the unit.
I can be pretty handy in that last year I tapped into the EAC 120v control to run a relay and turn on a force fan while the unit runs. I also happen to have an unused wire in the wall from the unit to the thermostat - so I just need to find the right place to get the C / 24 volt off of the unit. Anyone able to possibly guide me to the right place. I've got a PDF I found last year that goes with my unit, but too big to attach here. The link is http://site.famousparts.com/goodman/IO-137.pdf
I would appreciate any help or insight how I tap into the power supply of the unit and run to the thermostat as a C wire.
Thanks,
I can be pretty handy in that last year I tapped into the EAC 120v control to run a relay and turn on a force fan while the unit runs. I also happen to have an unused wire in the wall from the unit to the thermostat - so I just need to find the right place to get the C / 24 volt off of the unit. Anyone able to possibly guide me to the right place. I've got a PDF I found last year that goes with my unit, but too big to attach here. The link is http://site.famousparts.com/goodman/IO-137.pdf
I would appreciate any help or insight how I tap into the power supply of the unit and run to the thermostat as a C wire.
Thanks,
#31
Goodman uses the furnace body for C.
Connect the new thermostat C wire to a screw on the furnace body.
Connect the new thermostat C wire to a screw on the furnace body.
#32
Member
Join Date: Aug 2012
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Great info and thanks for that information. This makes it easy for me since I've got an extra wire already in the wall and just loose on each end.
Would you mind helping my feeble mind then! If the C is nothing more than ground - does that mean it just gives the thermostat the ability to pull the power out of the R wire at all times - the C - giving it the ability to complete the 24v circuit back to the unit at all times rather than just when the fan is on?
So really it always gets power from the R? I wasn't understanding - I thought the C was going to give me the circuit not just a "ground" - a way to complete that circuit.
Thanks !
Would you mind helping my feeble mind then! If the C is nothing more than ground - does that mean it just gives the thermostat the ability to pull the power out of the R wire at all times - the C - giving it the ability to complete the 24v circuit back to the unit at all times rather than just when the fan is on?
So really it always gets power from the R? I wasn't understanding - I thought the C was going to give me the circuit not just a "ground" - a way to complete that circuit.
Thanks !
#33
Member
Join Date: Jan 2013
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I used the wiring diagram provided in this thread by hvactechfw on 01-22-12 to connect my Nest thermostat to my Quadrafire natural gas stove with millivolt contacts for the thermostat. That diagram allowed me to successfully install my 24 v Nest thermostat to my millivolt stove without damage to either. The cost of the 120 v to 24 v transformer and the SPST Relay with a 24 v coil was less than $40. Thanks for the great advice.
#34
Member
Join Date: Jan 2010
Location: Illinois
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
WiFi thermostat for millivolt
I have a similar question to this thread that I am hoping hvactechfw can confirm and clarify. I plan on installing a Williams 3003622 direct vent wall furnace at my 3 season lake house. This is a millivolt system and this is a link to the installation manual for any questions http://e-wfc.com/pdf/Direct_Vent_Furnaces_IOM.pdf. This furnace will be used instead of existing electric baseboard heat. I want to install a Honeywell WiFi thermostat so that we can turn the heat on remotely and have the main part of the house up to 70 degrees when we arrive 3+ hours later. This is a link to the thermostat manual http://wifithermostat.com/assets/pdf...ish-French.pdf.
Referring to your post on installing a Nest thermostat on a millivolt system and the drawing that you posted on 1/22/12... will this work for my requirements above? It all sounds the same to me. If yes, can you 1) recommend part numbers for a 24vac transformer that is not overkill and a recommeded spst relay? and 2) can you add wire detail for the gas valve to relay connections. Does the wiring not matter? Same question on coil to thermostat side... can W and C go to either terminal on coil side?
Thank you in advance for sharing any expertise.
Referring to your post on installing a Nest thermostat on a millivolt system and the drawing that you posted on 1/22/12... will this work for my requirements above? It all sounds the same to me. If yes, can you 1) recommend part numbers for a 24vac transformer that is not overkill and a recommeded spst relay? and 2) can you add wire detail for the gas valve to relay connections. Does the wiring not matter? Same question on coil to thermostat side... can W and C go to either terminal on coil side?
Thank you in advance for sharing any expertise.
#38
Member
Join Date: Nov 2013
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Had a similar system with only HEATING and no cooling, and old thermostat just had the R and W connected with no C. I ended up getting the 24VAC transformer and hooked the wire up to the RC (didnt have a RH), hooked the old wires (comming from the furnace to the wall) up to the R and the W. I also UNJUMPED the RC & R on the thermostat to make sure the 24V wouldnt reach to my Millivolt system. Everything works fine. I did this on a WiFi Honeywell unit. (just figured i would post this since it seemed like a good thread)
#39
Member
Join Date: Jan 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
buzzing on 6azu2 spst relay
Regarding the wiring instructions by hvactechfw.
I have followed the directions for installing my Nest with millivolt fireplace. Everything is working just great. Thanks for providing such great instructions.
I am only having one issue. The Relay is buzzing. It is a brand new relay, and I used exactly what was specified.
I checked the voltage with the Relay completely wired, and I am getting 27.4 volts. I then check the voltage wiring the Relay direct to the transformer, (bypassing Nest, etc) and I am getting 27.7 volts - so the drop is very small.
I know sometimes Relays can buzz due to a voltage drop, and they can also buzz right out of the box. It wouldn't be a big deal, but it is loud, and the relay is Chattering also, which is causing the stove to turn on and off intermittently for one second at a time
Any ideas on what would be causing this? Could the Relay just be bad?
I have followed the directions for installing my Nest with millivolt fireplace. Everything is working just great. Thanks for providing such great instructions.
I am only having one issue. The Relay is buzzing. It is a brand new relay, and I used exactly what was specified.
I checked the voltage with the Relay completely wired, and I am getting 27.4 volts. I then check the voltage wiring the Relay direct to the transformer, (bypassing Nest, etc) and I am getting 27.7 volts - so the drop is very small.
I know sometimes Relays can buzz due to a voltage drop, and they can also buzz right out of the box. It wouldn't be a big deal, but it is loud, and the relay is Chattering also, which is causing the stove to turn on and off intermittently for one second at a time
Any ideas on what would be causing this? Could the Relay just be bad?
#40
Did you try running the relay directly from the transformer. If it chatters then..... replace it.
There are so many imitation/knockoff relays on the market it could just be defective.
There are so many imitation/knockoff relays on the market it could just be defective.