Wire size
#1
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wire size
I need to install a 70 amp 240 volt circuit(3 wire + ground) about 70 feet in length. I was looking at table 310.16 and if I read this correctly I can use #6 wire in conduit if I use one of the wire types specified for 194 degrees F(such as thhn). If I use a wire designated 167 degrees F then I need #4 wire? Am I reading this correctly.
Last edited by ednu99; 04-07-09 at 11:25 AM.
#2
Is this an instant water heater or welder the circuit is for? What is the full load amps of the device. What is the size of the main breaker. What other loads do you have? 70amps is a very large load to add to a residential situation. Wire size is only one of the factors that need to be considered. You say three wire plus ground. Is this a sub panel? Most 240v/70a loads would only require 2 wires plus ground.
Last edited by ray2047; 04-07-09 at 10:39 AM.
#3
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The 70 amps I quoted was the breaker size not the load. It's for a pc oven and the full load is 12,400 watts or around 52 amps. The neutral is needed to drive a light and small fan. The service panel is rated 200 amps and has the capacity to support this circuit.
#4
Is the fan and light part of the oven? Is this a detached building? Are there any other circuits to the building? A detached building can have only one circuit. If you already have power to the building you are going to need a sub panel. or is the panel in the building and this is commercial?
Just curious is this an oven specifically made for powder coating or a residential bake oven? What are the manufacturers instructions. If this oven is part of a stove and burners won't be used you may not need as much as you think.
Just curious is this an oven specifically made for powder coating or a residential bake oven? What are the manufacturers instructions. If this oven is part of a stove and burners won't be used you may not need as much as you think.
#5
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is the fan and light part of the oven? YES Is this a detached building? Are there any other circuits to the building? A detached building can have only one circuit. If you already have power to the building you are going to need a sub panel. or is the panel in the building and this is commercial? The service panel is in the building, it's not a subpanel.
Just curious is this an oven specifically made for powder coatingYes or a residential bake oven? No What are the manufacturers instructions. Custom made.If this oven is part of a stove and burners won't be used you may not need as much as you think.There are 4 elements rated at 3100 watts each. It will be drawing the 52 amps I mentioned.
Just curious is this an oven specifically made for powder coatingYes or a residential bake oven? No What are the manufacturers instructions. Custom made.If this oven is part of a stove and burners won't be used you may not need as much as you think.There are 4 elements rated at 3100 watts each. It will be drawing the 52 amps I mentioned.
#7
I think the #6 should be okay. Ampacity of #6 is 65A; 52A load * 125% continuous rating factor = 65A. Installing a 240V light and fan motor might be cheaper than pulling the #6 neutral.
#8
Member
Join Date: Feb 2009
Location: Iowa
Posts: 310
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If you're going to put this on a 70 amp breaker you will need to run #4's. As for your neutral you can drop down to #6 and your grounding wire can be #8. If you had this on a 60 amp breaker then you could run #6's, #8 for your neutral and #10 for your grounding wire. The way I read this is your full load is 52 amps. You will need to factor in the continuous load factor which is 125% continuous rating factor= 65a. You should put a 70 amp in this set up.
Jim
Jim
#9
Member
Join Date: Apr 2009
Location: Southeast USA
Posts: 43
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If the watts are bumped up to 15000 with the amps at 63 and the load factor bringing it to 78.75 amps, using #4 wire and 1 #6 neutral could a 80 or 90 amp breaker be used as long as the THHN wire was rated at 95 amps (90C)?
Thanks,
Grumple
Thanks,
Grumple
#10
Member
Join Date: Feb 2009
Location: Iowa
Posts: 310
Upvotes: 0
Received 0 Upvotes
on
0 Posts
JimBeer 4U2
#11
Member
Join Date: Apr 2009
Location: Southeast USA
Posts: 43
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So the circuit as described will work with an 80 amp breaker? Without any changes to wire size?
Thanks,
Grumple
Beer 4U2
#12
Member
Join Date: Feb 2009
Location: Iowa
Posts: 310
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Jim
#13
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What table or calculation are you referencing to come up with the 80 amp number? I would just like to understand how you determined this.
#14
Member
Join Date: Feb 2009
Location: Iowa
Posts: 310
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks!
Jim
#15
Member
Join Date: Apr 2009
Location: Southeast USA
Posts: 43
Upvotes: 0
Received 0 Upvotes
on
0 Posts
rukkus11,
Ok, I also see that in my Wiring Simplified book. One more question. Is the load factor applied only once for the breaker, or is it applied once for the wire AND once for the breaker? Thats all the questions I have. So if I want to run my pc oven at a max 15000 watts (5-3000 watt elements) plus a 120v light and a small low amp blower, the following will work:
2- #4 THHN wires Black for main loads
1- #6 THHN White for neutral
1- #8 THHN Green for ground
In a 1" conduit
80 amp circuit breaker
I am picking up the wire this morning.
Thanks for all your help,
Grumple
Beer 4U2
Ok, I also see that in my Wiring Simplified book. One more question. Is the load factor applied only once for the breaker, or is it applied once for the wire AND once for the breaker? Thats all the questions I have. So if I want to run my pc oven at a max 15000 watts (5-3000 watt elements) plus a 120v light and a small low amp blower, the following will work:
2- #4 THHN wires Black for main loads
1- #6 THHN White for neutral
1- #8 THHN Green for ground
In a 1" conduit
80 amp circuit breaker
I am picking up the wire this morning.
Thanks for all your help,
Grumple
Beer 4U2
Last edited by Grumple; 04-09-09 at 05:56 AM.
#16
Member
Thread Starter
Join Date: Jul 2007
Location: ohio usa
Posts: 141
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NEC book-310.16. This is based off the 75c chart. #4 is rated at 85 amps and you are allowed to use this as long as all terminals connections are rated at 75c. Most breakers are 60/75c rated and pretty sure the oven he's wiring up is 75c. Now for some reason if one of his terminals are only rated at 60c then he would have to use the 60c chart. Very hard to explain all of this over this thread and I didn't what to confuse anyone. Hope this may help some towards your question.
Thanks!
Jim
Thanks!
Jim
#18
Member
Join Date: Feb 2009
Location: Iowa
Posts: 310
Upvotes: 0
Received 0 Upvotes
on
0 Posts
rukkus11,
Ok, I also see that in my Wiring Simplified book. One more question. Is the load factor applied only once for the breaker, or is it applied once for the wire AND once for the breaker? Thats all the questions I have. So if I want to run my pc oven at a max 15000 watts (5-3000 watt elements) plus a 120v light and a small low amp blower, the following will work:
2- #4 THHN wires Black for main loads
1- #6 THHN White for neutral
1- #8 THHN Green for ground
In a 1" conduit
80 amp circuit breaker
I am picking up the wire this morning.
Thanks for all your help,
Grumple
Beer 4U2
Ok, I also see that in my Wiring Simplified book. One more question. Is the load factor applied only once for the breaker, or is it applied once for the wire AND once for the breaker? Thats all the questions I have. So if I want to run my pc oven at a max 15000 watts (5-3000 watt elements) plus a 120v light and a small low amp blower, the following will work:
2- #4 THHN wires Black for main loads
1- #6 THHN White for neutral
1- #8 THHN Green for ground
In a 1" conduit
80 amp circuit breaker
I am picking up the wire this morning.
Thanks for all your help,
Grumple
Beer 4U2
Jim