trane xl80 valve noise
I am getting a constant valve buzzing noise from the Johnson Controls G5308BG-7 gas valve on my Trane model #TDD060A936A0. It started off intermittently and is now steady when the burners are ignited. I took a voltage reading @ the valve and from the transformer and got 25.4(quality meter). Is the voltage to high? If it is would it be the transformer or something else involved with its function. All other furnace function is normal. If the voltage is ok I guess I should replace the valve Thanks Rolynn1
#2
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes
on
39 Posts
At 24.5 volts, the valve should not have any voltage problem. My guess is the coil on the valve is what's buzzing. Other than making sure all connections are clean & tight, about all you can do is to replace the valve.
#3
Member
Thread Starter
Join Date: Oct 2014
Location: United states of america
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Trane xl 80
Thanks for your reply but the V reading was 25.4. 1 higher than other threads were indicating. Is this still within acceptable operating limits?