Skuttle Humidifier to Goodman Furnace
|
|
-
01-25-09, 01:04 PM #1
Member
- Join Date
- Feb 2006
- Posts
- 28
Skuttle Humidifier to Goodman Furnace
I have a Goodman AEPF 4260 Furnace/Heat Pump and a Skuttle Humidifier. Wiring diagram says wires to R and humidistat but whenever I plug it in there's no voltage? :wall:Unhooked I have 24V. There's a jumper that had to be cut and I did that but nothing. Also hooked wire to another terminal and got power but I am afraid to leave it there as it might do damage to board. Thanks for any help.
-
01-26-09, 09:53 PM #2
Ok, one wire on R and where's the other one gong to?
What was the other letter you hooked up to and got power?-Jay
If you can do it, We can help.
-
01-27-09, 06:30 PM #3
Member
- Join Date
- Feb 2006
- Posts
- 28
goodman furnace, skuttle humidifier
The other terminal is marked humidstat, (supposed to be correct wire). The terminal that gave me power was O.
ThanksLast edited by mattherb; 01-27-09 at 06:31 PM. Reason: better explaination
-
01-27-09, 08:19 PM #4
Member
- Join Date
- Jan 2009
- Posts
- 61
Disconnect and stay away from the O wire. This is your cool active reversing valve. Wire up, from HVAC, terminals R and HUM to the humidifier and then to Humidistat.
-
01-28-09, 05:57 AM #5
Member
- Join Date
- Feb 2006
- Posts
- 28
goodman furnace, skuttle humidifier
yes, those are the 2 I used but no power. I scanned the wiring diagram if I can figure out how to post it, if not can I email to you?
Thanks
-
01-28-09, 06:26 AM #6
Member
- Join Date
- Jan 2009
- Posts
- 61
Send wiring diagram to:
removed e-mail address, either post it in your profile or spell it out like at dotLast edited by Jay11J; 01-28-09 at 10:39 AM.
-
01-28-09, 08:58 AM #7
Member
- Join Date
- Feb 2006
- Posts
- 28
goodman furnace/skuttle humidifier
diagram sent. Thanks for the effort!
-
01-28-09, 10:42 AM #8
I am unable to find a diagram for you unit.
If you know for sure HUM is 24 volts, then other wire goes to C./Com on the board.-Jay
If you can do it, We can help.
-
01-28-09, 02:27 PM #9
Member
- Join Date
- Feb 2006
- Posts
- 28
goodman
which diagram? I emailed the furnace one. from Removed e-mail address. Put them in your profile or spell it out like at dot com
Last edited by Jay11J; 01-28-09 at 03:52 PM. Reason: removed e-mail address.
-
01-28-09, 03:22 PM #10
Member
- Join Date
- Feb 2006
- Posts
- 28
so one wire to HUM and one to com? Great, thanks a lot Jay!
-
01-28-09, 03:53 PM #11
-
01-28-09, 05:17 PM #12
Member
- Join Date
- Feb 2006
- Posts
- 28
Goodman Furnace, Skuttle Humidifier
That works! You're the man Jay! the com terminal is the condensor? I measure 24volts either way, does it matter if one is to R and one to com or HUM and com?
-
01-28-09, 08:48 PM #13-Jay
If you can do it, We can help.