Posted By: Jay11J Sounds like you got a bad Auto Pilot control (white one). This should only light the pilot when there is call for heat.

What happens when you turn on the t-stat to call for heat?
Thanks for your reply! You're right, my assumption was wrong.

It seems to be the wiring rather than the control: I just figured out that if I press slightly on the 5 pin connector on the gas valve, the furnace fires up correctly. With pressure, it stops ticking when there is no call for heat by the thermostat (to answer your question, it ticked as well when there is a call for heat -- just more quickly at about twice the rate).

Should I just rewire that thing from scratch?