Cable bundled into Cantex PVC conduit?
Am installing a new subpanel , a short run from the service entrance ( approx. 12 feet) thru one wall , outdoor service to indoor sub.
Using 1 1/4" PVC with turns on it.
Can I bundle my cables 3- #2 copper, 1-8ga, thwn , and 1 10ga romex?
It will fit thru the turns ok , I bundled it about every foot tightly together with a few wraps of 2 " PVC electrical tape to be able to make it thru the PVC.
Is there a problem doing this?
The service is a 200 amp and the sub is a 125 amp on a 100 amp breaker.
The romex is for the AC unit to the service and not from the sub as before.
It will be tied to the existing 10ga. romex via junction box about the sub.
Using 1 1/4" PVC with turns on it.
Can I bundle my cables 3- #2 copper, 1-8ga, thwn , and 1 10ga romex?
It will fit thru the turns ok , I bundled it about every foot tightly together with a few wraps of 2 " PVC electrical tape to be able to make it thru the PVC.
Is there a problem doing this?
The service is a 200 amp and the sub is a 125 amp on a 100 amp breaker.
The romex is for the AC unit to the service and not from the sub as before.
It will be tied to the existing 10ga. romex via junction box about the sub.
#2
my cables 3- #2 copper, 1-8ga, thwn
1 10ga romex?
outdoor service to indoor sub
#3
Member
Thread Starter
Join Date: Apr 2016
Location: USA
Posts: 56
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You are correct Ray they are conductors, not cable.
The reason I used the 10ga romex is that I had it on hand.
Even though it is outside it technically isn't.
Its under a covered patio that is out of the elements of rain, snow and sun.
and the length of run out doors is about 3.5 feet.
I had the 1-1/4" PVC and it did fit but only when I bundled it.
Other than being in a close fitting conduit would there be a problem bundling 2 hots a neutral a ground and romex? all are new and insulated.
Ben
The reason I used the 10ga romex is that I had it on hand.
Even though it is outside it technically isn't.
Its under a covered patio that is out of the elements of rain, snow and sun.
and the length of run out doors is about 3.5 feet.
I had the 1-1/4" PVC and it did fit but only when I bundled it.
Other than being in a close fitting conduit would there be a problem bundling 2 hots a neutral a ground and romex? all are new and insulated.
Ben
#4
I can't think of reason this was needed . It will make it harder to radiate away any heat buildup. It may be a derating issue.
#5
Get rid of the cable and replace with two THWN. If it doesn't fit easily without bundling use a larger conduit.
Just because you had it is not a reason to not do it the best way. The very fact that you had trouble getting it in says the conduit is to small and the cable taking up too much room. Even if your AHJ accepts the NM-b in your case going with two THWNs instead of NM-b makes more sense and may give you room to pull everything without bundling. However me, I'd go with 1½" conduit. Cheap guarantee it is done the best way.
The reason I used the 10ga romex is that I had it on hand. I had the 1-1/4" PVC
#6
Member
Thread Starter
Join Date: Apr 2016
Location: USA
Posts: 56
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Will heed advise and get the larger conduit and use the THWN and get rid of romex, but think I will use 3 THWN , really do not want to use the #8 one as its ground for sub.
thanks
thanks
#7
think I will use 3 THWN , really do not want to use the #8 one as its ground for sub.
The romex is for the AC unit to the service and not from the sub as before.
#8
Member
Thread Starter
Join Date: Apr 2016
Location: USA
Posts: 56
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Got the 1-1/2 and 10gag THWN this morning. I am moving the double breaker to the service as I have lots more room in the service and there is limited space in the sub, so it was easy enough to move and leave more room in the sub for future additions
Thanks Ray.
Ben
Thanks Ray.
Ben