Shed power
Wiring my shed. 30 feet from my homes entrance panel. All I need is 5 outlets and 5 lights. No 240a ever. I have room for 2/30a breakers in entrance panel. My plan is to put a 30a breaker in the entrance panel, feeding a 10/3 conductor to a two place subpanel in my shed. Then put 2/15a breakers in that subpanel. One feeding my outlets, and one the light fixtures.
my question, is this Ok? Is it overkill? Is it Underkill?
my question, is this Ok? Is it overkill? Is it Underkill?
#2
Member
Why not just go with a double pole 15 or 20 amp breaker in your service panel with 14/3 or 12/3 feeding the shed? Use a DPST switch as a disconnect and feed your two circuits. With a panel you will need GEC with grounding rods.
#3
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes
on
230 Posts
If doing the 30A feed to the shed using a subpanel, as Astuff said you'll need a grounding electrode (rods). If going that route make the outlet circuit 20A. Also the 30A feed using 10/3 will need to be buried 18" if in conduit or 24" if direct bury. By using 10/3 you will have 240V available. To make sure we are on the same sheet of music, 10/3 is 4 conductors, 2 phase conductors, 1 neutral and 1 ground.
#4
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Goid suggestions. Turns out I only have room in my entrance panel for 2 single pole breakers. One across from the other at the bottom of the panel.
is it possible to split a 10/3 conductor between two opposing breakers? I've never seen that done before so seems like a long shot. I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?
is it possible to split a 10/3 conductor between two opposing breakers? I've never seen that done before so seems like a long shot. I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?
#5
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
In almost all cases circuit breakers installed "across" from each other are on the same "hot" bus and therefore cannot be used for a 240 volt (or multi-wire branch circuit) feed. What you MAY be able to do is to move the CB above one or the other of the spare slots to the other side of the panel and thereby have two spaces on different buses.
Unless that 12-2 cable you have is listed as type UF (underground feeder) you may NOT use it outside or underground, even if you place it in conduit.
Unless that 12-2 cable you have is listed as type UF (underground feeder) you may NOT use it outside or underground, even if you place it in conduit.
#7
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I think furd is right though. I may need to do some rearranging of my entrance.
Looks like I need to run 2 separate conductors from 2 separate 20a breakers. 20a minimum is code here for outbuildings. I'd like to have my 5 lights and 5 outlets on separate circuits if possible without running 2 separate conductors from my main panel. I really don' want the problem of adding 2 20a breakers and running 2 separate 12/2 conductors.
#8
If you move a single pole breaker you will have space for the two pole bresker. You could then run two hits and a neutral and ground.
#11
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My entrance panel is a 200a Cutler-Hammer 0f 2002 vintage. The 2 available spaces are able to accept tandem breakers. Not sure if that's acceptable or not. I've already fixed 2 double taps with tandems the previous homeowner did.
#13
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the heads up on the quad pole. By removing a single pole, I'm able to have space for the quad. Feeding the existing circuit, and allowing for my feed to the shed. Sounds like my best bet.
#14
I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?
#15
I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?
If the 12-2 is yellow it is NM-B cable and it cannot be used underground or outside. If it is UF-B (normally gray) it can be used underground or outside.