Shed power

Wiring my shed. 30 feet from my homes entrance panel. All I need is 5 outlets and 5 lights. No 240a ever. I have room for 2/30a breakers in entrance panel. My plan is to put a 30a breaker in the entrance panel, feeding a 10/3 conductor to a two place subpanel in my shed. Then put 2/15a breakers in that subpanel. One feeding my outlets, and one the light fixtures.
my question, is this Ok? Is it overkill? Is it Underkill?
 
  #2  
Old 12-04-17, 11:24 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
Why not just go with a double pole 15 or 20 amp breaker in your service panel with 14/3 or 12/3 feeding the shed? Use a DPST switch as a disconnect and feed your two circuits. With a panel you will need GEC with grounding rods.
 
  #3  
Old 12-04-17, 11:38 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes on 230 Posts
If doing the 30A feed to the shed using a subpanel, as Astuff said you'll need a grounding electrode (rods). If going that route make the outlet circuit 20A. Also the 30A feed using 10/3 will need to be buried 18" if in conduit or 24" if direct bury. By using 10/3 you will have 240V available. To make sure we are on the same sheet of music, 10/3 is 4 conductors, 2 phase conductors, 1 neutral and 1 ground.
 
  #4  
Old 12-05-17, 12:11 AM
T
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Goid suggestions. Turns out I only have room in my entrance panel for 2 single pole breakers. One across from the other at the bottom of the panel.
is it possible to split a 10/3 conductor between two opposing breakers? I've never seen that done before so seems like a long shot. I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?
 
  #5  
Old 12-05-17, 02:23 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
In almost all cases circuit breakers installed "across" from each other are on the same "hot" bus and therefore cannot be used for a 240 volt (or multi-wire branch circuit) feed. What you MAY be able to do is to move the CB above one or the other of the spare slots to the other side of the panel and thereby have two spaces on different buses.

Unless that 12-2 cable you have is listed as type UF (underground feeder) you may NOT use it outside or underground, even if you place it in conduit.
 
  #6  
Old 12-05-17, 05:32 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes on 230 Posts
A multiwire circuit requires a double pole breaker or two single pole breakers with a handle tie. So that eliminates the use of two single breakers across the panel from each other.
 
  #7  
Old 12-05-17, 12:20 PM
T
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think furd is right though. I may need to do some rearranging of my entrance.

Looks like I need to run 2 separate conductors from 2 separate 20a breakers. 20a minimum is code here for outbuildings. I'd like to have my 5 lights and 5 outlets on separate circuits if possible without running 2 separate conductors from my main panel. I really don' want the problem of adding 2 20a breakers and running 2 separate 12/2 conductors.
 
  #8  
Old 12-05-17, 12:24 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
If you move a single pole breaker you will have space for the two pole bresker. You could then run two hits and a neutral and ground.
 
  #9  
Old 12-05-17, 05:00 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes on 230 Posts
NEC does not allow 2 separate circuits to feed a detached structure. So two 12/2 on two separate breakers is a no no.
 
  #10  
Old 12-05-17, 05:15 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,329
Received 877 Upvotes on 740 Posts
A multiwire circuit is considered a single circuit and is allowed per NEC 225.30 (2014) The two hots need to be on opposite legs in the panel.
 
  #11  
Old 12-06-17, 10:05 AM
T
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
My entrance panel is a 200a Cutler-Hammer 0f 2002 vintage. The 2 available spaces are able to accept tandem breakers. Not sure if that's acceptable or not. I've already fixed 2 double taps with tandems the previous homeowner did.
 
  #12  
Old 12-06-17, 12:48 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes on 230 Posts
I don't believe Eaton (Cutler Hammer) has a tandem double pole breaker, only single pole tandems.. Eaton does have quad double pole, but that uses two full spaces next to each other.
 
  #13  
Old 12-07-17, 12:01 PM
T
Member
Thread Starter
Join Date: Dec 2017
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the heads up on the quad pole. By removing a single pole, I'm able to have space for the quad. Feeding the existing circuit, and allowing for my feed to the shed. Sounds like my best bet.
 
  #14  
Old 12-07-17, 01:50 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?
Sure..... if you only want a single 120v 20A circuit out there.
 
  #15  
Old 12-08-17, 06:21 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
I also have 100 feet of 12/2 in a shelf. Any chance of using that to feed my shed?

If the 12-2 is yellow it is NM-B cable and it cannot be used underground or outside. If it is UF-B (normally gray) it can be used underground or outside.
 
 