Install Ecobee 3 Lite - where to plug in PEK
Hello all! So I'm looking at the instructions of the Ecobee 3 Lite and none of it lines up with what I have in my furnace room.
Any ideas?
Pictures here https://imgur.com/a/REhAZ
Any ideas?
Pictures here https://imgur.com/a/REhAZ
Last edited by PJmax; 12-07-17 at 11:36 AM. Reason: added 1 pic from link
#2
Welcome to the forums.
The PEK doesn't get plugged in anywhere..... it gets wired in.
At the top of the board.... the orange arrow will be the C.
Will you be replacing stat 1, 2 or 3 ?
You only need three wires and some look like 3 wire cables.
You WILL need a voltmeter for testing.
We need to label your TT terminals...... W and R.
Right now....the red and white wires are arbitrarily connected.
The PEK doesn't get plugged in anywhere..... it gets wired in.
At the top of the board.... the orange arrow will be the C.
Will you be replacing stat 1, 2 or 3 ?
You only need three wires and some look like 3 wire cables.
You WILL need a voltmeter for testing.
We need to label your TT terminals...... W and R.
Right now....the red and white wires are arbitrarily connected.
#4
That's because that thermostat is designed for a furnace.
You don't have a furnace.... you have a boiler.
You don't have a furnace.... you have a boiler.
#7
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wow - so sorry. On mobile I totally missed it!
Ok - so I’ll check this all as soon as I get back home.
Unfortunately i I don’t understand the questions - I’m not up on the jargon (TT, stat), so I'll have to look those up.
Really sorry. I'm a new and first time home owner. I don't know everything about the house.
Thanks so much for trying to help
Ok - so I’ll check this all as soon as I get back home.
Unfortunately i I don’t understand the questions - I’m not up on the jargon (TT, stat), so I'll have to look those up.
Really sorry. I'm a new and first time home owner. I don't know everything about the house.
Thanks so much for trying to help
#8
I drew the orange arrow in for C.
At the top right side of the board are where the three thermostats connect. You will need to determine which one you are replacing. The stats are currently connected to TT labeled terminals on the board. Those T's will be relabeled R and W as we test them.
At the top right side of the board are where the three thermostats connect. You will need to determine which one you are replacing. The stats are currently connected to TT labeled terminals on the board. Those T's will be relabeled R and W as we test them.
#10
You are only showing a 3 zone/thermostat zone control panel.
A 4th thermostat would mean some type of kluge wiring.
Hopefully the stats you want to change go to the zone controller.
A 4th thermostat would mean some type of kluge wiring.
Hopefully the stats you want to change go to the zone controller.
#11
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just what I was afraid of. I see the 4th is connected differently and not within that relay box.
I'll map it all out and post back. Thanks for the help.
I'll map it all out and post back. Thanks for the help.
#12
I went back to look at your other pictures. It looks like the 4th stat connects directly to the aquastat. There is no way to connect a wifi stat directly to the aquastat. You'd need an aux source of 24vac to run it. That would require an additional 24vac transformer and a relay or 4 wires between that aquastat area and the stat.
#13
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#17
Remove the two wires from the stat terminals you are working on. If you aren't ready to connect the new stat yet.... just use thermostat 1 location. Using a voltmeter set to next scale over 24VAC. Connect either probe to the COM where the orange arrow is. Touch the other probe to A or B. The A and B repeat on all three locations. Tell me which letter.... A or B..... measures 24vac.
#18
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sweet, as posted before - all the A terminals are the R (hot) wires.
Also, yes - there is a 3rd wire in the bundle, so I can connect those to the C terminal - right?
Also, yes - there is a 3rd wire in the bundle, so I can connect those to the C terminal - right?
#19
Yup......... you're the man.
Use a Sharpie and write it over the T's.
I will now put this board pic in my archives for the next person that asks.
Use a Sharpie and write it over the T's.
I will now put this board pic in my archives for the next person that asks.
#20
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No you are!
Awesome! Thanks so much for the help!
Only other thing I'm not sure how to do is the stat on the aquastat. How I handle that one exactly.
Back to YouTube!
Thank you again
Awesome! Thanks so much for the help!
Only other thing I'm not sure how to do is the stat on the aquastat. How I handle that one exactly.
Back to YouTube!
Thank you again
#21
This is my recommendation and is based on the exact way I do the installation. You only need a small 24vac 10va transformer. You can use any size from 24vac 10-40 va. You can get a transformer that connects to an electrical box or one that is attached to an electrical plate or even use a plug-in wall wart.
This is one of the exact plug-in ones I use.....
MG-ELECTRONICS-MGT2420-TRANSFORMER
All kinds of 24vac transformers that will work.....
keywords=24vac+hvac+transformers
This is one relay... the 290... it's fine. My diagram is the 293. Both work.
Little different connection..... PACKARD-PR290Q-Relay-Coil-Contacts
Easy three wire connection.
This is one of the exact plug-in ones I use.....
MG-ELECTRONICS-MGT2420-TRANSFORMER
All kinds of 24vac transformers that will work.....
keywords=24vac+hvac+transformers
This is one relay... the 290... it's fine. My diagram is the 293. Both work.
Little different connection..... PACKARD-PR290Q-Relay-Coil-Contacts
Easy three wire connection.
#22
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok - 1st Ecobee is up! Yay!!!
Alright - this next one I’d like to do the best way recommended.
So if I got the wall plug in, I may have an issue - no outlets there. I don’t want to string wires all over
If I picked up a 24v transformer, where would I connect it in relation to the connection stream?
where do I feed the transformer power from and then how would I connect the stat power and the C circuit?
Thanks again!
Alright - this next one I’d like to do the best way recommended.
So if I got the wall plug in, I may have an issue - no outlets there. I don’t want to string wires all over
If I picked up a 24v transformer, where would I connect it in relation to the connection stream?
where do I feed the transformer power from and then how would I connect the stat power and the C circuit?
Thanks again!
#23
No receptacle near the boiler ?
Maybe best to get a transformer that connects to an electrical junction box.
You need the power near the boiler where your three wire cable is located.
Maybe best to get a transformer that connects to an electrical junction box.
You need the power near the boiler where your three wire cable is located.
#24
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok - so just want to make sure I understand. I need the transformer only? Don’t need transformer and relay - right?
The transformer is only two wires, so how would I create a C wire for 3 wires?
The transformer is only two wires, so how would I create a C wire for 3 wires?
#25
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here is another thought. Could I relocate one of the stats I'm not swapping out from the control box (garage) to the aquastat and move the stat from the aquastat to the control box (where garage stat was) and be all done?
#26
It looks like the 4th stat connects directly to the aquastat. There is no way to connect a wifi stat directly to the aquastat. You'd need an aux source of 24vac to run it. That would require an additional 24vac transformer and a relay or 4 wires between that aquastat area and the stat.
Relay and transformer for 3 wires or just a transformer with 4 wires.
I don't see a reason why the zones can't be swapped..... stat and circulator wiring.
#27
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just wanted to say - THANK YOU!
I've completed the swap and rewiring of the stats - the downstairs, which was on TT 2 and the Bedroom, which was on the aquastat. That was fun - never did that kind of stuff before.
I've bundled the C wires necessary for both TTs and everything is working!
I did have a scare and I had to go to Lowes! LOL.. When I saw no green light on the control board after flipping the power on - my heart stopped. I thought I fried the board.. Turns out I accidentally confused the stats and wiring colors and put the C wire on the W wire, which was plugged into the stat in the Bedroom and it blew out the fuse. Quick fix - thank gosh! OMG - what a bad bad feeling to have.
So I will return on a slow day at the house and get all of these colors consistent by color. But I know what they are for now - I labeled them
Thanks again for all of the help and patience. Couldn't have done it without your help @pjmax!
I've completed the swap and rewiring of the stats - the downstairs, which was on TT 2 and the Bedroom, which was on the aquastat. That was fun - never did that kind of stuff before.
I've bundled the C wires necessary for both TTs and everything is working!
I did have a scare and I had to go to Lowes! LOL.. When I saw no green light on the control board after flipping the power on - my heart stopped. I thought I fried the board.. Turns out I accidentally confused the stats and wiring colors and put the C wire on the W wire, which was plugged into the stat in the Bedroom and it blew out the fuse. Quick fix - thank gosh! OMG - what a bad bad feeling to have.
So I will return on a slow day at the house and get all of these colors consistent by color. But I know what they are for now - I labeled them
Thanks again for all of the help and patience. Couldn't have done it without your help @pjmax!
#29
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
One last thing. I wanted to swap out the Garage (zone 1) and move that to the aquastat, but when I went to the control box, I noticed a second black wire connected. See the picture https://imgur.com/liccQVH
So I decided not to mess with anything too advanced, and I just used the Downstairs (zone 2) - it didn't have any extra wires.
But I was just thinking and realized that I'm going to have to deal with this issue soon, because I was planning to put an Ecobee Downstairs. Zone 3 is already being used, and zone 2 is the new Bedroom stat we just swapped in.
The Garage has a blower unit that sends the heat out as it blows. Is this why the second black wire is connected?
Let me know if you need pictures to help with what I'm trying to explain.
Sorry if I keep resurrecting this thread. I know you want it to die! lol
So I decided not to mess with anything too advanced, and I just used the Downstairs (zone 2) - it didn't have any extra wires.
But I was just thinking and realized that I'm going to have to deal with this issue soon, because I was planning to put an Ecobee Downstairs. Zone 3 is already being used, and zone 2 is the new Bedroom stat we just swapped in.
The Garage has a blower unit that sends the heat out as it blows. Is this why the second black wire is connected?
Let me know if you need pictures to help with what I'm trying to explain.
Sorry if I keep resurrecting this thread. I know you want it to die! lol
#30
Hmmmmm...... I've seen that picture before.
I see the two black wires on the Circ 1 hot terminal. I don't know what that is for. If you are saying that is the garage zone (Z1) and it has a fan forced hydronic unit...... one black could be for a pump and the other could be for the fan. That isn't the ideal way to set up that kind of heater but it probably works.
Usually there is a thermostat strapped to the hot water pipe behind the hydronic heater. When the return line gets hot.... the fan starts. This keeps from blowing cold air around.
I see the two black wires on the Circ 1 hot terminal. I don't know what that is for. If you are saying that is the garage zone (Z1) and it has a fan forced hydronic unit...... one black could be for a pump and the other could be for the fan. That isn't the ideal way to set up that kind of heater but it probably works.
Usually there is a thermostat strapped to the hot water pipe behind the hydronic heater. When the return line gets hot.... the fan starts. This keeps from blowing cold air around.
#31
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yea, you called it - again. That's what we're dealing with.
So should I be looking to hook it up the right way or is there a way to hook it up - safely - to the aquastat? or is that a no-no?
Should I be working towards connecting it the right way - what you described? I don't understand it, but I'll have to learn.
So should I be looking to hook it up the right way or is there a way to hook it up - safely - to the aquastat? or is that a no-no?
Should I be working towards connecting it the right way - what you described? I don't understand it, but I'll have to learn.
#32
There are two negatives with the way it is now.
1 - it allows the fan to blow cold for several minutes. That's not bad.... just a little wasteful.
2 - it takes the fan power off the zone controller and the controller isn't really rated to have a pump and a fan on an output. Three pumps is already putting a load on that controller. Actually... I don't think those little style pumps draw a lot.
Putting that load on the boiler aquastat would be worse.
You could change the switched line to the garage to an always live line and use a strap on thermostat like in the link below. If you search around there are other similar stats for less. This strap on stat monitors the temp of the return line of the heater. It turns the fan on and off based on the set temp. Usually it's set around 110-120 degrees.
Honeywell-L6006C1018-Aquastat-Controller/dp/B0006UPLAS
1 - it allows the fan to blow cold for several minutes. That's not bad.... just a little wasteful.
2 - it takes the fan power off the zone controller and the controller isn't really rated to have a pump and a fan on an output. Three pumps is already putting a load on that controller. Actually... I don't think those little style pumps draw a lot.
Putting that load on the boiler aquastat would be worse.
You could change the switched line to the garage to an always live line and use a strap on thermostat like in the link below. If you search around there are other similar stats for less. This strap on stat monitors the temp of the return line of the heater. It turns the fan on and off based on the set temp. Usually it's set around 110-120 degrees.
Honeywell-L6006C1018-Aquastat-Controller/dp/B0006UPLAS
#33
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Let me make sure I explained that blower and how it works today.
Its connected per the pictures. It has a stat that I use to monitor and keep the temp in the garage at a set temp. When it’s below that, it kicks on.
Same me thing you suggested still applies? If so, I’ll check that out. Definitely want to do clean and best method work.
Its connected per the pictures. It has a stat that I use to monitor and keep the temp in the garage at a set temp. When it’s below that, it kicks on.
Same me thing you suggested still applies? If so, I’ll check that out. Definitely want to do clean and best method work.
#34
Member
Thread Starter
Join Date: Dec 2017
Location: United States
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I guess you already answered my question - I'm just re-reading it now and realizing that.
I may bring in someone to assist with this. I think this is more advanced then I can handle.
Thanks again! Safe to archive this one.
I may bring in someone to assist with this. I think this is more advanced then I can handle.
Thanks again! Safe to archive this one.
#35
The threads basically archive themselves. They don't get closed unless they are very old and brought back. They stay in the archives forever.