Gas furnace goes off – excessive gas flow?
Hi Folks, I am facing quite new and unusual (for the HVAC pros in my area) issue: my gas furnace won't stay lit unless I adjust the gas flow control arm on the main pipe that goes in the furnace. Once lowered, it is working quite steadily and does not go off.
Any suggestions on WHY is this happening and how to fix it (need it running @ its fullest, huh:?), would be highly appreciated!
Any suggestions on WHY is this happening and how to fix it (need it running @ its fullest, huh:?), would be highly appreciated!
#2
A better explanation is needed. What is the gas flow control arm and what does it look like and do?. What is the age of the furnace and make and model number. Pictures would be helpful
#4
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hi, thanks a million for your prompt response(s). The gauge, the arm is on the pic. The furnace is 15 yo, Carrier. Cheers, V
Last edited by Vlado; 02-08-18 at 05:27 PM.
#6
Welcome to the forums.
That IS a problem and would suggest a defective gas valve.... in particularly the regulator stages. If you have a technician.... have him check the manifold gas pressure. If you don't have a tech..... check with your gas supplier. They employ some good field technicians and will take care of the problem without gouging or trying to sell you a new furnace.... unless it's absolutely necessary.
That MUST be addressed as soon as possible.
That IS a problem and would suggest a defective gas valve.... in particularly the regulator stages. If you have a technician.... have him check the manifold gas pressure. If you don't have a tech..... check with your gas supplier. They employ some good field technicians and will take care of the problem without gouging or trying to sell you a new furnace.... unless it's absolutely necessary.
That MUST be addressed as soon as possible.
#7
Member
Running the furnace like that is potentially dangerous, and can cause damage to the furnace. It must be fixed ASAP.
Closing that valve down like that is not a fix.
Closing that valve down like that is not a fix.
#9
Member
Improper gas flow/pressure/volume.
Improper use of that valve. It isn’t designed to be a throttle or operate in a mid position like that.
Improper use of that valve. It isn’t designed to be a throttle or operate in a mid position like that.
#11
Member
You need to start by
Taking gas pressure readings on the input and manifold side of the valve.
Measure temperature rise across the heat exchanger.
Taking gas pressure readings on the input and manifold side of the valve.
Measure temperature rise across the heat exchanger.
#12
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Sure. It is a malfunctioning pressure regulator incorporated in the combination gas valve. It MAY be simply in need of adjustment if it has always been this way or it may need to have the combination gas valve replaced and the pressure regulator properly adjusted. Generally speaking this is NOT a DIY job.
#15
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Guys, a quick update on the issue. The Christin HVAC, Inc. rep came to fix it, measured the gas pressure, adjusted it just a little bit and said it should be alright now. Not! The problem is still there, and once he realized that it's something else, he said it is thermocouple, which need to be replaced. Asked for $311 on top of $187 that I already paid... Asked him how likely is that the thermocouple is causing this, given that it has been replaced a month ago and the problem is still there... So $187 wasted, thinking of suing these idiots for guesstimating and making 3 holes in furnace... Cheers!
#16
Member
That does not seem to have the symptoms of a thermocouple problem.
What was the gas pressure and what did he adjust it to?
What was the gas pressure and what did he adjust it to?
#17
Member
V,
The job of the thermocouple is to tell the gas valve it's OK to open. It has nothing to do with regulating gas pressure.
As PJ suggested that is the job of the gas valve which has a regulator built in.
If the thermocouple was your problem by not sensing the heat to open the gas valve you would have no fire at all.
Unless I'm missing something I can't understand why they keep looking at the thermocouple and not taking gas pressures and look at the gas valve.
Just my thoughts, hope this helps a little.
The job of the thermocouple is to tell the gas valve it's OK to open. It has nothing to do with regulating gas pressure.
As PJ suggested that is the job of the gas valve which has a regulator built in.
If the thermocouple was your problem by not sensing the heat to open the gas valve you would have no fire at all.
Unless I'm missing something I can't understand why they keep looking at the thermocouple and not taking gas pressures and look at the gas valve.
Just my thoughts, hope this helps a little.
#18
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Guys, thanks a lot for all of your responses. Please see the pic. The MF drilled three holes in the system for no reason! Is that too bad for the furnace? New concern now
#20
Member
I thought the other service guy checked gas pressure and said it was ok? 4.06 is much too high.
#21
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hi Folks,
Just posted an update and it disappeared from this thread. In a few words, this was the same guy, who adjusted the pressure, drilled 3 holes and left, telling me it was all bad thermocouple. He said, the diameter of the pipe in the couple was not right. Do you think the thermocouple's bandwidth may be an issue? Thanks a lot. I think they just sucked my money and showed their back.
Just posted an update and it disappeared from this thread. In a few words, this was the same guy, who adjusted the pressure, drilled 3 holes and left, telling me it was all bad thermocouple. He said, the diameter of the pipe in the couple was not right. Do you think the thermocouple's bandwidth may be an issue? Thanks a lot. I think they just sucked my money and showed their back.
#22
Member
To repeat what was said earlier in this thread, the thermocouple has nothing to do with gas pressure.
Why did he drill holes in the flue pipe? To test the combustion gasses?
Is the unit still functioning properly? Is the gas valve open fully?
Why did he drill holes in the flue pipe? To test the combustion gasses?
Is the unit still functioning properly? Is the gas valve open fully?
#23
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have no idea of WHY he drilled the hole – he never asked, and when I realized that, it was too late – suing these mfs. The problem is still there, and the gas valve is open on 2/3s. thank you!
#24
Member
I’d call another company to take a look. Or call the service manager and complain.
Either way it still needs to be addressed ASAP.
Either way it still needs to be addressed ASAP.
#25
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 11
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hi Roughneck77, thank you – called and complained the same day, spoke with the manager. He told me that I paid $99 just for the visit and diagnostics, and although incorrect, and the problem persists, they adjusted the valve for an extra $88. Rip-off. Any suggestions? Before I take them to court, need your words of wisdom and advice. Thanks