I just have a question. I am installing my own a/c/ unit. I need to know when I am installing the unit on the furnace. The unit seems like its to close to the heat part of the furnace. can it be to close?
#4
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes
on
39 Posts
A/C install
Yes it can be too close. Most manufacturers specify 6-8" between the drain pan & the heat exchanger. If the furnace is oil fired & one is availabe, install a metal drain pan under the A coil.