Outside unit fan comes on but not compressor
#1
Member
Thread Starter
Join Date: May 2005
Posts: 20
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Outside unit fan comes on but not compressor
I have a Goodman 2ton unit about 10 yrs old when you set the Tstat for cool the inside fan comes on, but when you go outside the condensor unit fan is on but i've never heard it "click" to get the compressor to come on. I checked with my meter and I had 24 volts at the contactor relay, it was contacted but nothing happens. I had a friend put gauges on it and he said it has freon in it the head pressure was 200 low pressure was 120 not running.. I noticed alot of rust on the terminals on the capacitor, I carefully moved the wires on and off of the capacitor trying to make a better connection but to no help there still compressor won't come on.. I now have the contactor relay off and am looking for a new one today, anyone have any advice to whats wrong.. is there a reset on my unit ? or a fuse ? any help would be terriffic...
thanks
Zeke
thanks
Zeke
#2
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Zeke
Have the capacitor checked. The fan side could be good & the compressor side bad, if you have a dual capacitor like most Goodmans. Another possibility is a wire burned off at the terminal block on the compressor. For some unknown reason, Goodman equipment (in my experience) seems to have this problem more than some other manufacturers.