Compressor drawing more amps than should

I had my furnance checked for the winter and the tech checked the A/C unit and said the compressor was drawing between 8-11.4 amps, double what it should. Said the unit may not make it through next summer.

Is he correct? Does it mean the unit will eventually fail?

Thanks
 
  #2  
Old 10-07-05, 07:13 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Did he check the charge/pressure??
 
  #3  
Old 10-07-05, 07:19 PM
J
Member
Join Date: Oct 2005
Location: USA
Posts: 1,017
Upvotes: 0
Received 0 Upvotes on 0 Posts
That doesn't make sense. One half of 8-11.4 is 4 to 5.7 amps. That's a mighty small compressor. Is it a 1 ton compressor ?
 
  #4  
Old 10-08-05, 06:10 AM
flynavydiesel's Avatar
Member
Thread Starter
Join Date: Apr 2004
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
He did not check the charge, and it is a 1-ton compressor. small builders grade.
 
  #5  
Old 10-08-05, 06:42 AM
J
Member
Join Date: Oct 2005
Location: USA
Posts: 1,017
Upvotes: 0
Received 0 Upvotes on 0 Posts
High running amps could mean a bad compressor. But there are other causes which include; overcharged system, bad/weak capacitor, low line voltage, or dirty condenser coils. Everything else needs to be checked before the compressor is condemned. Also, these conditions left uncorrected will shorten compressor life.
Waiting until the compressor burns out is not such a good idea because of the possibility of system contamination.
 
  #6  
Old 10-08-05, 07:06 AM
flynavydiesel's Avatar
Member
Thread Starter
Join Date: Apr 2004
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for that info, the tech just said the unit should be replaced. Easy way tomake money. I will have the unit properly checked to see what is going on.
 
  #7  
Old 10-08-05, 10:56 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,315
Upvotes: 0
Received 0 Upvotes on 0 Posts
On the condensing unit is a label. Post the model #, Serial #, and it may have "RLA" for the compressor.
 
 