Outdoor AC unit stays on even with open contactor
Help.
Ran AC for 1st time this year. Outdoor unit when I woke up was iced up as indoor unit had stopped. I had to pull the breaker to get it to stop. Contactor is not stuck shut, it is open. When I put breaker back in, unit outside immediately starts. Thermostat disconnected. What would be causing the unit to start with the contactor open?
After further investigation, I noticed i have 2 orange wires going to the compressor. 1 goes to the bottom of the contactor, 1 to the top. If i disconnect bottom orange, unit operates normal(tstat controls it, doesnt run always as before). I put the orange with the other orange at the top of the contactor. Works fine. Any ideas?
Received 41 Upvotes
Condensing unit stays on
Usually inside the wiring cover is a wiring diagram. If you can find it, trace the wires & make sure they are the same as the diagram. If they are & the unit still stays on, the contactor points could be welded together.