Contactor Good...no Action

Neither compressor or condensor fan will come on....the contactor is engaging....Any guidance will be appreciated.
 
  #2  
Old 06-23-06, 02:19 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 1 Vote on 1 Post
Wink

Do you read any power on the in-- side and the out--- side of the contactor?????

ED
 
  #3  
Old 06-23-06, 02:31 PM
R
RGM
RGM is offline
Member
Thread Starter
Join Date: Jun 2006
Posts: 9
Received 0 Votes on 0 Posts
Yes sir....I have 120 volts at each of the two wires on the connector from the 240 feed
 
  #4  
Old 06-23-06, 02:51 PM
M
Member
Join Date: Feb 2006
Location: USA
Posts: 929
Received 0 Votes on 0 Posts
But do you have 240 volts across the contactor? If you are checking each leg of the contactor to neutral then because of the wiring scheme you may be reading the same phase when checking each leg of the contactor. You NEED to have 240 there somewhere...
 
  #5  
Old 06-23-06, 02:53 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 1 Vote on 1 Post
Wink

Do you read 220V going into the contactor and 220V comeing out of it?????

ED
 
  #6  
Old 06-23-06, 03:05 PM
R
RGM
RGM is offline
Member
Thread Starter
Join Date: Jun 2006
Posts: 9
Received 0 Votes on 0 Posts
Each of the 120v readings were to ground, reading across the connections I have 240 volts...Just for more information, the condensor fan turns freely and the connector does close when the tstat is on, but nothing else happens except for a very low "buzzing" when the connector closes.
 
  #7  
Old 06-23-06, 03:11 PM
Former Member's Avatar
Member
Join Date: May 2006
Location: US
Posts: 786
Received 0 Votes on 0 Posts
next step is to replace the dual capacitor. Most likely your culprit.
 
  #8  
Old 06-27-06, 02:17 PM
R
RGM
RGM is offline
Member
Thread Starter
Join Date: Jun 2006
Posts: 9
Received 0 Votes on 0 Posts
Replaced cap, still would not start. Hooked up a SPP6 kicker and it started....Shut it down, took out the kicker and it restarted fine. Guess I will keep the kicker handy for possible restarts should it go down again.
Thanks to all who replied, I appreciate the guidance that was given.
 
  #9  
Old 06-27-06, 02:23 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 18,386
Received 1 Vote on 1 Post
Wink

Id let the little kick start on the unit.

ED
 
  #10  
Old 06-27-06, 02:53 PM
R
RGM
RGM is offline
Member
Thread Starter
Join Date: Jun 2006
Posts: 9
Received 0 Votes on 0 Posts
Being the curious type, after the unit restarted I took it out to see if it would still start up. When the thing stops again (I'm pretty sure it will), I will put it back in and leave it.
Thank you....this board provides a wealth of information.
 
 