outside a/c fan will not shut off
Old 06-24-06, 06:00 AM
R
stopped by my mothers the other day and she told me her outside central a/c fan will not shut off. turned tstat way up.still ran...turn tstat to off...still ran....the blower motor shuts down...and the unit blows cold just fine......the outside ubit will not shut down unless i flip the breaker....any help would be welcome...thanks....btw..it is a trane unit.not sure of model
Old 06-24-06, 06:23 AM
nap's Avatar
nap
nap is offline
New Member
Received 1 Vote on 1 Post
Sounds like the relay on the condensor has welded its' contacts.
Are you a bit tech and electrical savvy?
Old 06-24-06, 11:34 AM
Ed Imeduc's Avatar
Wink
You dont say .Does the compressor run to?? If so then bugs could have got up there in the contactor points and burnt like said. Dont let the outside unit run with out the inside fan on.
ED
Old 06-25-06, 12:15 PM
I have the same problem with my unit.
My question is: How can I find contactor points in my AC unit?
I have Day&Night model, probably 20+ years old.
Thank you for all your help.
Michael
Old 06-25-06, 01:47 PM
condenser fan motor
most units are wired to the conpressor contactor. but some have a control relay. have to trace wires back from fan motor are look at the wiring diagram and see where the wires go to. probably the relay needs to be replaced