Please Help (Compressor Electrical Inop)
I just got home and realized the house was unnaturally warm. I went upstairs and checked the thermostat its set for 77 but the temp is 85. I then went out to the breaker box and the breaker for the compressor was off. It wont allow me to reset it. Any advice would be very welcome.
#2
Member
Join Date: Oct 2005
Location: USA
Posts: 1,017
Upvotes: 0
Received 0 Upvotes
on
0 Posts
When you say "it won't allow me to reset it", what do you mean? The correct procedure for resetting a breaker is to move it to the "off" position and then turn it to the "on" position. If it immediately trips again, you have a short somewhere between the breaker and including the compressor. If on the other hand, the breaker handle feels loose, doesn't move, or smells burnt, you likely have a bad breaker.
If you are comfortable working around high voltage, we can help you diagnose further.