carrier heat pump noisy start up


  #1  
Old 02-14-08, 08:51 AM
S
Member
Thread Starter
Join Date: Feb 2008
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
carrier heat pump noisy start up

have 1 yr. old carrierheat pump model 25hbr336a0030010. when it starts it sounds like the whole unit will vibrate itself to death for 5 to 10 seconds. seems to run an abnormally long time no colder than it is. the installer has serviced it and says that everything is fine,that it is a scroll compressor is going into defrost and that they are noisy. is this a common problem with carrier? the way this thing sounds(wakes you up in the night) i dont see how a blanket around the compressor is going to stop the noise. any suggestions?
 
  #2  
Old 02-14-08, 12:24 PM
Ed Imeduc's Avatar
Member
Join Date: Aug 2002
Location: Mountain Williams Missouri
Posts: 17,505
Upvotes: 0
Received 1 Upvote on 1 Post
Wink

Might check does it have a crankcase heater on it and does it work? If not might put one on it.
 
  #3  
Old 02-14-08, 06:45 PM
M
Member
Join Date: Jan 2008
Location: Tennessee
Posts: 438
Upvotes: 0
Received 0 Upvotes on 0 Posts
AC Compressor Noise

This residential compressor should be getting it's heat from one leg wired through a single pole contactor if someone has mistakenly replaced it with a two pole contactor or it is factory setup with a two pole contactor then it must have a crankcase heater that is working or liquid refrigerant will migrate to the bottom and cause major failure.
 
 