Smile american standard allegiance 16 Comfort R ?

what is the correct way to wire this system with the freedom 80 furnace, in order to activate comfort r

Do you need to jumper Y to O
Do you need to jumper R to O

presently I have it wired with the am standard 803 thermostat
y1 to y and y to stage 1 on the outside unit, (yellow wire, on the outside unit)

and Y2 to Bk to stage 2 on the outside unit(yellow wire with stripe)

all dip switches appear to be correct I am just trying to confirm the tstat - furnace- outdoor unit wiring

My installer does not seem to know?

thanks, in advance
 
  #2  
Old 04-10-08, 06:57 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by cepjr
Do you need to jumper R to O
R and O is the jumper for the ramping.

Factory BK jumper on the furnace's board needs to be cut.

presently I have it wired with the am standard 803 thermostat
y1 to y and y to stage 1 on the outside unit, (yellow wire, on the outside unit)

and Y2 to Bk to stage 2 on the outside unit(yellow wire with stripe)
That is correct.
 