hot shot cap for stuck compressor

How is the hot start cap wired in with the existing start run cap. If the compressor breaks free, remove or leave the hot shot in place?
 
  #2  
Old 05-20-08, 05:39 PM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 9,500
Received 68 Upvotes on 62 Posts
It is not that simple.
A "stuck" compressor is really a seized compressor..........it's not like it will be freed and then be ok.

It might be possible that a hard start relay gets it running but it will have to remain installed.
A typical hard start relay wires across the run cap terminals but you need to follow the instructions that come with it.
 
  #3  
Old 05-20-08, 08:08 PM
G
Member
Thread Starter
Join Date: Dec 2006
Location: south carolina usa
Posts: 165
Upvotes: 0
Received 0 Upvotes on 0 Posts
GreggH

Thanks for the reply.
Then evidently there is more to this package than just another hang on capacitor. Your mention of a relay is a factor I did not know about, and evidently takes the hot shot out of service once the compressor starts. This is just an assumption of course. Thanks, Tom
 
 