Command-Aire Thermostat Change-out


  #1  
Old 05-25-08, 04:52 AM
M
Member
Thread Starter
Join Date: May 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Command-Aire Thermostat Change-out

Hi, I have Command-Aire model SWP 351EA water source heat pump in my apartment. I want to replace the original thermostat model CM260A with a Totaline Model P474-0100. This one has auto change-over feature from cool to heat and heat to cool.

The original is a four (4) wire. Can anyone tell me the correct connections to use on the Totaline?
 
  #2  
Old 05-26-08, 05:45 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
I am not able to find any info on your current t-stat.

When you look at the sub-base, what wire is hooked up to what letters on the current sub-base?
 
  #3  
Old 05-27-08, 04:34 PM
M
Member
Thread Starter
Join Date: May 2008
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wiring

Hi Jay11j,

The thermostat wiring to heat pump is as follows:

Rc is connected to R (Random Start [24 VAC])
G is connected is connected to G (Fan)
Y is connected to Y2 (Compressor)
O is connected to Y1 (Reversing valve)

There is also a jumper on the thermostat between Y and W.

The heat pump is a water source type which provides both cooling and heat. The original thermostat was a manual change over type. The Totaline is an auto changeover type.

I hope the above info helps.
 

Last edited by mb300e; 05-27-08 at 04:45 PM. Reason: Omission.
  #4  
Old 05-27-08, 07:07 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by mb300e View Post
The thermostat wiring to heat pump is as follows:

Rc is connected to R (Random Start [24 VAC])
G is connected is connected to G (Fan)
Y is connected to Y2 (Compressor)
O is connected to Y1 (Reversing valve)

There is also a jumper on the thermostat between Y and W.
Heat pump to T-stat
R to R (may need a jumper wire at t-stat.)

G to G

Y1 to O

Y2 to Y


The heat pump is a water source type which provides both cooling and heat.
Is there back up heat source on the heat pump?
 
  #5  
Old 08-17-14, 10:45 AM
K
Member
Join Date: Aug 2014
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hello MB300, I see you helped someone else out a while back with a Command_aire thermostat. I want to install a new programmable White-Rodgers thermostat and cannot figure out the wiring. My existing thermostat has R (red wire), G(green wire), Y1 (blue wire), Y2 (white wire) terminals. The new White Rodgers unit has O/B, Y, G, W2, C, L, R terminals. Can you help? Many thanks, Fred
 
  #6  
Old 08-17-14, 11:23 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,420
Received 75 Upvotes on 68 Posts
Looks like MB was assisted by Jay.
Can you post the connections at the heat pump?
It looks like their Y1 was connected to O at the heat pump. If this is the case your new thermostat will support your system.
 
  #7  
Old 08-17-14, 12:11 PM
K
Member
Join Date: Aug 2014
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks, but he mentions a jumper. The old thermostat has no jumper so where would a jumper go in the new one. Let me shoot J a message too.
 
  #8  
Old 08-17-14, 12:14 PM
K
Member
Join Date: Aug 2014
Location: usa
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hello Jay, I see you helped someone else out a while back with a Command_aire thermostat. I want to install a new programmable White-Rodgers thermostat and cannot figure out the wiring. My existing thermostat has R (red wire), G(green wire), Y1 (blue wire), Y2 (white wire) terminals. The new White Rodgers unit has O/B, Y, G, W2, C, L, R terminals. Can you help? Many thanks, Fred
 
 