Neither fan nor compressor comes on

neither the fan nor compressor comes on at outside unit when called for but if I push contactor in with my meter they both come on and work fine any suggestions.
 
  #2  
Old 09-09-08, 09:33 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,315
Upvotes: 0
Received 1 Upvote on 1 Post
You mention a meter. Do you have 24 vac at the contactor coil on a call for cooling ??
 
  #3  
Old 09-09-08, 10:35 AM
B
Member
Thread Starter
Join Date: Sep 2008
Location: louisiana
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
where should i check for the 24 volts at on the contactor i get 120+ on each leg and 240 when on botyh legs when i kick it on the contactor will close but only temporarily if held down both the fan and compressor run fine
 
  #4  
Old 09-09-08, 11:08 AM
B
Member
Thread Starter
Join Date: Sep 2008
Location: louisiana
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
if i test across the contact where both end closes i get 0 the small control wires or red and black wire on either side they read from 2 to 4 volts only places i could think of checking really dont know what else to do
 
  #5  
Old 09-09-08, 11:12 AM
B
Member
Thread Starter
Join Date: Sep 2008
Location: louisiana
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
could i use the contactor and or capacitor for a trane unit i have at another property this unit is a frigidaire unit
 
  #6  
Old 09-09-08, 11:25 AM
B
Member
Thread Starter
Join Date: Sep 2008
Location: louisiana
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
i can def say there is no 24 volts anywhere on the system all control wires are running no voltage or up to around 4 volts
 
 