New HVAC Thermostat - Need help with wiring
#1
Member
Thread Starter
Join Date: Dec 2008
Location: Orlando, FL
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
New HVAC Thermostat - Need help with wiring
I have a Goodman PHK 036-1A Electric Heat / A/C All-in-one unit that has 6 wires running to my thermostat.
I am moving from a Simple Comfort (SC2201) thermostat to a Honeywell RTH230B Programmable Thermostat.
The wiring on the original SC2201 was as follows:
BLACK -> O
WHITE -> W (Heating Call?)
GREEN -> G (Fan?)
BLUE -> Y (Cooling Call?)
RED -> R (Heating or AC Call?)
WHITE -> C (24VAC Common/Return?)
These are my best guess notes from various sources on the net. Note that there are 2 white wires.
The new Honeywell has no instructions for wiring the unit to a 6 wire lead (there are only 5 terminals on the subblock).
The Honeywell says the wiring should be as follows:
Rh -> Heating Power Supply
Rc -> Cooling Power Supply
W -> Heating Signal
Y -> Cooling Signal
G -> Fan
I am really banging my head against the wall on this one. I would love to be able to hook this up myself as oppose to hiring an A/C contractor to come out and do it for $100 in under 5 minutes.
Any suggestions, comments, thoughts would be greatly appreciated.
Happy Holidays.
I am moving from a Simple Comfort (SC2201) thermostat to a Honeywell RTH230B Programmable Thermostat.
The wiring on the original SC2201 was as follows:
BLACK -> O
WHITE -> W (Heating Call?)
GREEN -> G (Fan?)
BLUE -> Y (Cooling Call?)
RED -> R (Heating or AC Call?)
WHITE -> C (24VAC Common/Return?)
These are my best guess notes from various sources on the net. Note that there are 2 white wires.
The new Honeywell has no instructions for wiring the unit to a 6 wire lead (there are only 5 terminals on the subblock).
The Honeywell says the wiring should be as follows:
Rh -> Heating Power Supply
Rc -> Cooling Power Supply
W -> Heating Signal
Y -> Cooling Signal
G -> Fan
I am really banging my head against the wall on this one. I would love to be able to hook this up myself as oppose to hiring an A/C contractor to come out and do it for $100 in under 5 minutes.
Any suggestions, comments, thoughts would be greatly appreciated.
Happy Holidays.
Last edited by cbentl1; 12-23-08 at 06:38 PM. Reason: Confusing line removed.
#2
Member
Join Date: Jan 2008
Location: Tennessee
Posts: 438
Upvotes: 0
Received 0 Upvotes
on
0 Posts
thermostat help
If this new stat is digital it is a power stealing model, or if it is a mechanical stat either way it does not need a common to operate. Eliminate the wire going to the C terminal and make sure the new stat works with electric heat. If this is strictly a gas heat thermostat it will not call for your fan to run on a call for heat so read the instructions carefully.
#3
Member
Join Date: Dec 2008
Location: N. GA
Posts: 91
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The Honeywell says the wiring should be as follows:
Rh -> Heating Power Supply
Rc -> Cooling Power Supply
W -> Heating Signal
Y -> Cooling Signal
G -> Fan
Notice the lack of th "O" wire. It seems to be a gas heat T-Stat. You need to take it back and get one for a heat pump.
R= Supply of 24v to T-stat Rc&Rh should be jumpered
W= Heat (AUX or EMR)
Y= Cooling
G= Fan
O/B = Reversing valve, goodman is more than likely a fail in heat so use the"O" terminal
C= Common
There are your six wires.
You say you have 2 whites? Trace them down and ID them.
Good Luck & Happy Holidays
Rh -> Heating Power Supply
Rc -> Cooling Power Supply
W -> Heating Signal
Y -> Cooling Signal
G -> Fan
Notice the lack of th "O" wire. It seems to be a gas heat T-Stat. You need to take it back and get one for a heat pump.
R= Supply of 24v to T-stat Rc&Rh should be jumpered
W= Heat (AUX or EMR)
Y= Cooling
G= Fan
O/B = Reversing valve, goodman is more than likely a fail in heat so use the"O" terminal
C= Common
There are your six wires.
You say you have 2 whites? Trace them down and ID them.
Good Luck & Happy Holidays
Last edited by Mr Happy; 12-24-08 at 07:26 AM. Reason: clarification
#4
Member
Join Date: Jan 2009
Location: ga.
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
hvac help
I just bought a foreclosure and i guess the thermostat was a family heirloom ...lol anyway the previous owner took it and left 6 unlabeled wires hanging out the wall. green, red, blue, white, orange, yellow, on my thermostat i have y1, w/b, y/o, rh, rc, g ... the unit is a goodman ARUF036-001-1 inside and a goodman cple36-1a outside .... ANY Help ??
thanks
thanks
#5
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes
on
0 Posts
blaskrk
your inside somebody elses thread on a stat problem and it makes for confusion just start a thread next time to isolate your situation better.on your problem hopefully you can pick up the wire IDs from the connection in the furnace......industry standard to stat is R/RED/TR HOT...G/GREEN/FAN...Y1/YELLOW/COOL...W/WHITE/HEAT