A/C fan stopped working blowing air, troubleshoot?

The other day i noticed my AC blowing straight air and I went outside and noticed the fan isn't working at all. When i turn on the AC it blows cool air for a few minutes then turns warm. It runs with the normal sound but then a hissing sound comes on after couple mintues.

I need some advice on where to troubleshoot. thanks.

Model is a Trane XE1000

I'm not that familiar with the AC, so any detailed help would be appreciated.


LP
 
Sponsored Links
  #2  
Old 05-26-09, 08:01 PM
D
Member
Join Date: Aug 2007
Posts: 2,021
Received 0 Votes on 0 Posts
At the outdoor unit the fan is not running when you have the system turned on for cooling? What about the compressor, is it running? It's hard to follow your explanation. Divide it up into the outdoor unit is ...... the indoor unit is ..... Thanks.
 
  #3  
Old 05-27-09, 05:30 PM
L
Member
Thread Starter
Join Date: May 2009
Posts: 2
Received 0 Votes on 0 Posts
Originally Posted by daddyjohn View Post
At the outdoor unit the fan is not running when you have the system turned on for cooling? What about the compressor, is it running? It's hard to follow your explanation. Divide it up into the outdoor unit is ...... the indoor unit is ..... Thanks.
when i turn on the A/C, the indoor and outdoor units turn on and cool air runs for a few minutes, but the fan doesn't run on the outside unit and the tube into the outside unit is cold.

Also the outside unit runs for a few minutes, then there is a hissing noice come from it.

I appreciate the response.

LP
 
  #4  
Old 05-27-09, 05:39 PM
pflor's Avatar
Member
Join Date: Dec 2007
Location: U.S.A.
Posts: 1,127
Received 0 Votes on 0 Posts
To rephrase what you just said (correct me if I misunderstand you) --> On the outdoor unit, the fan AND compressor motors BOTH start, but after a few minutes the compressor remains running but the blower stops.

If this is the case, you seem to have a case of a defective condenser fan motor. Replace

VERY HARMFUL to the compressor to allow it to continue operating under this condition. Don't run your unit, you could lose your compre$$or
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: