Question Gurgling a/c

Whenever the condenser turns on or off, I hear gurgling. This unit uses 410a, my old unit was r22 and for 24 yrs never did this. It was contractor installed, but he says this noise is normal????? Help
 
  #2  
Old 07-18-09, 03:47 PM
S
Member
Join Date: Sep 2008
Location: Long Island
Posts: 695
Upvotes: 0
Received 0 Upvotes on 0 Posts
your dealing with a freon now that runs 3X what the old R-22 ran on the condenser and the liquid line so when it shuts off it has to equalize the 2 pressures and that might be liquid going back into the condenser...your old r-22 ran 240-260 psi and 65 to 75 psi on real hot days you can do an easy 700psi plus on the condenser with the new stuff
 
  #3  
Old 07-18-09, 08:01 PM
T
Member
Join Date: Dec 2005
Location: USA
Posts: 173
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by sminker View Post
your dealing with a freon now that runs 3X what the old R-22 ran on the condenser and the liquid line so when it shuts off it has to equalize the 2 pressures and that might be liquid going back into the condenser...your old r-22 ran 240-260 psi and 65 to 75 psi on real hot days you can do an easy 700psi plus on the condenser with the new stuff
I'm not sure if the higher pressure is causing his noise. But the new refrigerant 410A runs about 1.5X higher, not 3X than R22. So a unit running 260 on R22 would be about 420 with R410A.
 
  #4  
Old 07-21-09, 05:48 AM
B
Member
Thread Starter
Join Date: Jul 2009
Location: pa.
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanx for the reply. So this is a normal occurrence. I guess we were just use to the other unit.
 
 