blowing 50 amp time delay fuses


  #1  
Old 07-29-09, 11:02 AM
F
Member
Thread Starter
Join Date: Jul 2009
Location: ca.
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
blowing 50 amp time delay fuses

It`s been very hot lately. I.E. over 100 degrees. I blew a fuse on my service to my compressor last friday. Now the same side blew again yesterday. Around 10 days later. Any ideas?
 
  #2  
Old 07-29-09, 11:25 AM
dun11's Avatar
Member
Join Date: Feb 2009
Location: Local
Posts: 753
Upvotes: 0
Received 1 Upvote on 1 Post
You can take an amp draw at the compressor to see if its pulling high amps, also chk all line voltage conections from panel to load side of contactor.
 
  #3  
Old 07-29-09, 01:26 PM
D
Member
Join Date: Aug 2007
Posts: 1,851
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also check the fuse clips for tightness, ie- how well they grasp the fuse.
 
  #4  
Old 07-29-09, 01:51 PM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,606
Received 28 Upvotes on 27 Posts
What size fuses are specified on the compresser namplate?

Also, check the voltage at the contactor with and without the compresser running. Maybe your utility's voltage is running low in the hot weather? That will increase motor amps.
Doug
 
 