Goodman AC - condenser fan not starting


  #1  
Old 08-09-09, 04:02 PM
M
Member
Thread Starter
Join Date: Mar 2006
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Goodman AC - condenser fan not starting

I am able to get the fan to run after pushing it. The unit does not seem to be cooling though.

If I'm reading threads correctly, this points to the start capacitor, correct?

THe unit has a 40.0/5.0 MFD oval dual run capacitor.

Are the AC capacitors on Grainger all I need? They are quite a biut cheaper that some of the prices I see on HVAC websites.

Run Capacitor,5 MFD,370 VAC,Oval - Capacitors - Motor Supplies - Motors : Grainger Industrial Supply

Is this the same as the dual run type here?

Capacitors
 
  #2  
Old 08-09-09, 06:05 PM
Skip4661's Avatar
Member
Join Date: Dec 2008
Location: West Michigan
Posts: 255
Upvotes: 0
Received 0 Upvotes on 0 Posts
  #3  
Old 08-09-09, 06:53 PM
H
Member
Join Date: Nov 2002
Location: Massachusetts
Posts: 1,731
Received 1 Upvote on 1 Post
Run Cap

sure sounds like it, with the power off, try spin the blade with a screw driver, it should coast freely. If not, the motor is toast.
 
  #4  
Old 08-10-09, 05:46 PM
M
Member
Thread Starter
Join Date: Mar 2006
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
turned out it WAS the run capacitor. All is good now.
 
 