Air handler new motor wiring help


  #1  
Old 09-29-09, 09:01 AM
M
Member
Thread Starter
Join Date: Sep 2008
Location: Miami
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Air handler new motor wiring help

I opened up the Air-handler and found the blower wheel bad (My Previous Post). It was wobbling and thats reason for noise. Since its little old (1993), I decided to replace Motor, Wheel and Capacitor. I purchased the parts from local Rheem supplier and after getting home I realized the new motor has different wiring.

My old motor had only 3 wires (Brown, Orange, Black). Brown and Orange connected to Capacitor and Black to Power I believe. The new motor has 5 wires ( Brown, Brown, Purple, Yellow & Black). I understand the Brown & Brown will now connect to Capacitor and black to same old spot, but I don't know where the Purple wire goes and Yellow if that also needs to be connected.

Also the parts store guy gave a 900 rpm motor with 25 mfd cap as opposed to 825 rpm and 15 mfd cap existing items. He said the Rheem recommends the new motor.

  • Does it matter if I change the motor and capicitor?
  • The Capacitor has no markings. Does it matter which direction its connected ?

Help is really appreciated.

Below are the images for old/new motor wiring and connection diagrams.







 

Last edited by miamikk; 09-29-09 at 09:36 AM.
  #2  
Old 09-29-09, 10:11 AM
mattison's Avatar
Member
Join Date: Mar 2003
Location: Cinti, OH
Posts: 5,315
Upvotes: 0
Received 0 Upvotes on 0 Posts
The differant colors are for differant voltages. What is the voltage supplied to the motor? What are the voltage ranges for the new motor.

Example: New motor 120/208
Yell/Blk would be for 120
Pur/Blk would be for 208

Your new capacitor will not have the wire going to the breaker. Only the 2 browns will be on it. The black will go to the relay and either the purple or yellow will go straight to the breaker where the old orange wire went.
 
  #3  
Old 09-29-09, 12:35 PM
M
Member
Thread Starter
Join Date: Sep 2008
Location: Miami
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
I just updated the pictures with old/new motor information, wiring diagrams and also the Air Handler wiring diagrams.

I would really appreciate if someone can let me know the connections for new motor.
 
  #4  
Old 09-29-09, 12:50 PM
dun11's Avatar
Member
Join Date: Feb 2009
Location: Local
Posts: 753
Upvotes: 0
Received 1 Upvote on 1 Post
Its exactally what "Mattison" said, you will use the Purple and cap the Yellow.
 
  #5  
Old 09-29-09, 03:03 PM
M
Member
Thread Starter
Join Date: Sep 2008
Location: Miami
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you for both of you. I connected the 2 browns to Capacitor, black to same old position (relay) and purple to orange. That did fix the problem and the Air handler works fine and air blows like crazy.

I have a new problem. The outside unit does not turn on now. I will start a new thread as its with control wiring.

Once again thankyou for the help.
 
 