Honeywell RTH7600 Thermostat Installaton w/Trane XE1000


  #1  
Old 10-02-09, 01:30 PM
D
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
Honeywell RTH7600 Thermostat Installaton w/Trane XE1000

Here's what I have:

Trane XE1000 Heat Pump
Trane TWE060C5FC1 Air Handler
???? WTS0702(F) Heat Unit
Trane Thermostat (Weathertron - BAYSTAT240)

I am installing a Honeywell RTH7600 TouchScreen Thermostat

Closely following the manual and some tips online here is how I have wired the RTH7600:

WEATHERTRON HONEYWELL
BAYSTAT240 WIRE RTH7600

B black C
G green G
Y yellow Y
O blue O/B | W
- N/A jmp|-RC
R red jmp|-R
__________________________________

W white L3 | Aux
- N/A Y2 | E
- orange -
T brown -
F N/A -
Note: The layout is BAYSTAT240 - WIRE - RTH7600
(The forum doesn't keep my formatting unfortunately)

So the system seemed to be running fine and behaving ok except the other day I noticed that the outside compressor is running ALL the time. And it did not do this until I installed the new thermostat. So what could be wrong with how I wired the thermostat?
 
  #2  
Old 10-02-09, 05:57 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Can please redo on how you did it.

Example.

Old-------New
R----------R/Rc
C-----------C
G----------G


ect..
 
  #3  
Old 10-02-09, 06:46 PM
D
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, here it is:

WEATHERTRON----------------- HONEYWELL
BAYSTAT240--------WIRE--------RTH7600

--------B---------------black-------------C
--------G--------------green-------------G
--------Y---------------yellow------------Y
--------O---------------blue--------------O/B | W
-------N/A--------------N/A---------------jmp|-RC
--------R----------------red---------------jmp|-R
__________________________________

--------W--------------white-------------L3 | Aux
--------N/A------------N/A---------------Y2 | E
--------N/A------------orange-----------N/A
--------T---------------tan(brown)-------N/A
--------F---------------N/A---------------N/A
Need some [CODE] tags in this forum so things stay formatted.
 
  #4  
Old 10-02-09, 07:12 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Everything is wired up correct.

Make sure the Y wire is not touching R.

If it still running, undo the Y wire and see if that stops the unit outside.

Also, Do you know what your KW rating on the air handler? Reason I asked is you don't have E wired up.
 
  #5  
Old 10-02-09, 07:20 PM
D
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, I thought I had the wiring right. I'm wondering if the contactor is maybe acting up. It's 14 years old and original. I've replaced all the caps last year but thought the contactor was still ok. Maybe not.

Anyway, the air handler is rated at 6A. And the heater unit is 7kw.
It's a multi-stage heat. Heat pump and emergency strips.
 
  #6  
Old 10-02-09, 07:31 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
You have on bank of heat strip? If yes, then you need to add a jumper between Aux and E on the T-stat.

if you have more than one bank, then you need to add the unused t-stat wire to E and go to the air handler and wire E to W2 at the air handler.
 
  #7  
Old 10-02-09, 08:41 PM
D
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have one bank of strips so I'll add the jumper Aux to E.
I'm going to replace the contactor and that should fix the continuous compressor run problem.
 
  #8  
Old 10-03-09, 05:46 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sounds like a plan. Let us know if you have anyy other questions.
 
  #9  
Old 01-11-10, 09:20 PM
D
Member
Thread Starter
Join Date: Jan 2008
Location: USA
Posts: 20
Upvotes: 0
Received 0 Upvotes on 0 Posts
I just now noticed that I had the air handler model number wrong in this thread; it should be:

Trane TWE060C15FC1 Air Handler
 
 