Cased coil installed directly on furnace?


  #1  
Old 10-22-09, 01:34 PM
S
Member
Thread Starter
Join Date: Oct 2009
Location: Akron Ohio
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Cased coil installed directly on furnace?

Am installing a Goodman CAPF3636B6 cased coil with a Goodman GMV950453BXa 95% gas furnace positioned to work as an upflow unit. My specific question is in regards to the installation of the cased coil. Should it be installed directly on top of the furnace or should a small duct transition piece be fabricated? The coil plenum opening is designed to fit right over the furnace plenum opening (and does fit) but there is no way to attach the furnace plenum "tabs" to those of the coil itself. I am thinking it is just supposed to sit on the furnace, be secured in place with a few pieces of trunk duct straps and then mastic sealed where the finished surface of the furnace meets the finished surface of the cased coil unit.

I have done about 4 weeks worth of reading/calculating to make sure the system is installed correctly and this is about the only factor of the installation I cannot find any information on. Any opinions will be welcomed.
 
  #2  
Old 10-23-09, 08:11 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,420
Received 75 Upvotes on 68 Posts
The coil is usually installed directly over the furnace.
A transition between them would improve your ability to clean and inspect it though.
 
  #3  
Old 10-24-09, 06:04 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Houston204 View Post
A transition between them would improve your ability to clean and inspect it though.
All the cased coil I've seen are easy to get to, just pop the front cover off, and there you are. Unless I have not come across one that you are talking about?
 
  #4  
Old 10-24-09, 08:58 AM
S
Member
Thread Starter
Join Date: Oct 2009
Location: Akron Ohio
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
The cased coil does have a front inspection plate so no issue with accessing it. It also has a double drip collection system so one of which is a high temperature rated plastic (rated up to 300 degrees) so I don't foresee ever having to access the drip pans.

The main reason I asked about this was because I assumed if they were meant to fit together from the factory there would be some obvious connections points to secure the coil and a method of sealing the connection to ensure no air leaks.

I guess I will just set the coil on the furnace, secure it however is easiest and seal the seam between the 2 pieces with regular duct mastic.

Thanks for the input guys
 
  #5  
Old 10-24-09, 09:22 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
That can work okay on a gas furnace, however, oil furnaces with large heat exchangers near the top of the furnace should be installed on a transition at least 6" above the furnace.

Otherwise, there would be an airflow restriction with a lot of back-pressure & turbulence.

A large portion of the velocity & static pressure is lost before it enters the evaporator & the duct system.

Do a Google search on the above oil furnace problem.
 
  #6  
Old 10-24-09, 12:45 PM
S
Member
Thread Starter
Join Date: Oct 2009
Location: Akron Ohio
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
I thought the issue with coils and oil furnaces was the heat. I never would have figured coil restriction would be an issue with oil furnaces since they do produce such hot air and thus require fewer CFM to heat.

Why would a 6" transition make a difference for flow? If the size of the opening on the furnace doesn't change and the size of the inlet on the coil doesn't change why would a 6" gap between the two have any bearing on that?

I did read that a transition piece between and UNCASED coil and furnace is necessary but didn't find any info on the matter regarding cased coils.

Thank you for the input fellas.
 
  #7  
Old 10-25-09, 04:24 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,420
Received 75 Upvotes on 68 Posts
I usually dread cleaning these coils. It always feel like I'm going to see some white smoke before I can access the dirty side of it.

 
  #8  
Old 10-25-09, 05:38 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
oh .. duh! Yeah, you are right about that!
 
  #9  
Old 10-26-09, 02:44 PM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
Arrow 6" provides room for more air to flow between the HT/EX

Originally Posted by shane21 View Post
I thought the issue with coils and oil furnaces was the heat. I never would have figured coil restriction would be an issue with oil furnaces since they do produce such hot air and thus require fewer CFM to heat.

Why would a 6" transition make a difference for flow? If the size of the opening on the furnace doesn't change and the size of the inlet on the coil doesn't change why would a 6" gap between the two have any bearing on that?
It has a huge bearing because it provides room for the air to flow between the huge oil heat exchanger & the coil.

I did read that a transition piece between and UNCASED coil and furnace is necessary but didn't find any info on the matter regarding cased coils.

Thank you for the input fellas.
It is because the huge heat exchanger comes close to the top of the furnace & forces the airflow to the outer portion of the furnace.

Therefore, the airflow velocity hits the bottom of the evaporator coil drain pans & causes excessive back-pressure.

Below the evaporator coil is the worst place to lose velocity and generate back-pressure.

It is a real blower & airflow killer.

Where the duct system needs the velocity and static pressure is at the diffusers.
 
  #10  
Old 10-27-09, 02:04 PM
S
Member
Thread Starter
Join Date: Oct 2009
Location: Akron Ohio
Posts: 194
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by HVAC RETIRED View Post
It has a huge bearing because it provides room for the air to flow between the huge oil heat exchanger & the coil.
So even though there is no where for the air to go with a 6" tall duct support (the exact same size as the furnace supply plenum and cased coil "intake side") it still helps reduce back pressure? I guess I don't understand how that helps since the same amount of air still has to travel through the same size openings. I understand how change of direction - like elbows - add flow restriction and back pressure but the furnace-to-coil connection involves no change of direction.

If you don't want to explain it to me can you give me a site or two that further explains this?
 
  #11  
Old 10-31-09, 06:02 PM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
Test that oil furnace scenario airflow both ways

Originally Posted by shane21 View Post
So even though there is no where for the air to go with a 6" tall duct support (the exact same size as the furnace supply plenum and cased coil "intake side") it still helps reduce back pressure?

I guess I don't understand how that helps since the same amount of air still has to travel through the same size openings. I understand how change of direction - like elbows - add flow restriction and back pressure but the furnace-to-coil connection involves no change of direction.
Sorry, but in this scenario it does involve changes of direction & a lot of back-pressure.

My brother's little 1.5-Ton system split-system is NOT delivering even half the required airflow due to the E-Coil being installed directly on top of the furnace. Yes, I measured the airflow.

If you don't want to explain it to me can you give me a site or two that further explains this?
Sorry, I don't check my gmail very often, so maybe kept U waiting?

The huge heat exchanger very near top of furnace is either octagonal or round & takes up the entire center area of the furnace.

This causes a restricted area that creates back-pressure & a lot of turbulence before the air can even enter the evaporator coil intake area.

Maybe someone can make a drawing illustrated what that does to airflow. That causes the loss of velocity & there is nl transition area long enough to regain static so it's all trapped prior to entry i to the coil.

For one thing, that extreme back-pressure will also unload the blower wheel further reducing airflow.

U don't understand how that can cause a restriction? Wow.

Do several Google & Yahoo searches with different key words for this specific problem, include "oil furnace" in it!

On this DIY Forum, I'm not allowed to post links to my non-commercial web pages!

All U have to do is test an oil furnace scenario, "directly on top of the furnace & then 6" above the furnace on a transition," that I have described & U will know what it does to airflow!
 

Last edited by HVAC RETIRED; 10-31-09 at 06:21 PM. Reason: Test airflow both ways!
  #12  
Old 03-01-10, 05:07 PM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
What Two Oil Furnace mfg'ers Say Coil...

Originally Posted by shane21 View Post
I thought the issue with coils and oil furnaces was the heat. I never would have figured coil restriction would be an issue with oil furnaces since they do produce such hot air and thus require fewer CFM to heat.

Why would a 6" transition make a difference for flow? If the size of the opening on the furnace doesn't change and the size of the inlet on the coil doesn't change why would a 6" gap between the two have any bearing on that?

I did read that a transition piece between and UNCASED coil and furnace is necessary but didn't find any info on the matter regarding cased coils.
Thank you for the input fellas. - shane21
First, oil furnaces have a very large heat exchanger very near the top of the furnace which blocks direct entry through the evaporator.

Additionally, most oil furnace blower's blow from the side of the furnace across that huge heat exchanger, rather from the bottom like a gas furnace.

Here is also what Two oil furnace mfg'ers say about mounting the coil:

Regal & Hallmark & nearly all Oil Furnaces - Installation manuals
Boyertown Furnace Products Boyertown Furnace
Download the installation & service manuals
To find the information
below; Use within the pdf search: at least 6” above
Or, use pdf down arrow to P-8 & scroll down a-ways...
http://www.boyertownfurnace.com/Prod...nual042909.pdf

If the oil furnace is used in connection with summer air conditioning the evaporator coil must be installed at least 6” above the oil furnace for proper airflow. Distances less than 6” will result in decreased airflow. - mfg'ers'
Make sure outlet supply takeoffs are NOT blocked by the coil. In all cases, refer to the manufacturers’ data for static pressure losses to ensure the ESP - system static pressure does not exceed 0.5” WC.
 
  #13  
Old 03-10-10, 05:02 PM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
Oil furnace - a-coil height

Originally Posted by shane21 View Post
I thought the issue with coils and oil furnaces was the heat. I never would have figured coil restriction would be an issue with oil furnaces since they do produce such hot air and thus require fewer CFM to heat.

Why would a 6" transition make a difference for flow? If the size of the opening on the furnace doesn't change and the size of the inlet on the coil doesn't change why would a 6" gap between the two have any bearing on that?

I did read that a transition piece between and UNCASED coil and furnace is necessary but didn't find any info on the matter regarding cased coils.
Thank you for the input fellas.
Consider that if you sit the evaporator directly on top of a huge oil furnace heat-exchanger the entire entry area would be blocked, there would be NO airflow,.

Now think about only 2-inches above it, - there'd be very little airflow & huge static back-pressure; plus most squirrel cage blower wheels would begin to unload.

A Major Oil Furnace Airflow Problem Fix
Regal & Hallmark & nearly all Oil Furnaces - Installation manuals
Boyertown Furnace Products Boyertown Furnace
Download the installation & service manuals from ABOVE LINK BELOW LINK MAY NOT WORK!
http://www.boyertownfurnace.com/Prod...nual042909.pdf
To find the information below; Use within the pdf search: at least 6” above
Or use down arrow to P-8 & scroll down a-ways...

Or use down arrow to P-8 & scroll down a-ways...

"If the oil furnace is used in connection with summer air conditioning the evaporator coil must be installed at least 6” above the oil furnace for proper airflow. Distances less than 6” will result in decreased airflow."
Make sure outlet supply takeoffs are NOT blocked by the coil. In all cases, refer to the manufacturers’ data for static pressure losses to ensure the total system static pressure does not exceed 0.5” WC.
 
  #14  
Old 03-13-10, 08:44 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 664
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Houston204 View Post
I usually dread cleaning these coils. It always feel like I'm going to see some white smoke before I can access the dirty side of it.

On the upflow furnace, all the debris will be on the inside/underside, so you have to remove that cover plate & try to get past all the tubing!

That is why, when coils are installed directly on top of furnaces, we pump down & valve off the refrigerant lines, & then remove the coil to clean it. (Costly)

Also, using a transitions allows us to use a (SP) probe before (& after) the coil for static pressure testing.

Also, mfg'ers often list CFM airflow ratings according to the static pressure drop across (before & after) the coil.

Therefore, use an ample transition above the furnace for the coil mounting.
 
 