Motor Starter Keeps Tripping

Hi, I'm having trouble with one of our air handlers at work. It has a 5 hp motor and 2 belts. It was running ok for a long time. I just changed the filters and noticed that the belts were worn so I replaced them, as I do on all the other 3 units we have. The fan was running better and actually holding the access door on with the suction from the fan but now after it runs for about a half hour, I have to reset the motor starter, then it runs again for about a half hour or 45 min, then the same thing. Did I change something by replacing the belts? I put the same ones in AP37's. Any suggestions?
Thanks,
Joe
 
Sponsored Links
  #2  
Old 03-23-10, 07:14 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,384
Received 11 Votes on 9 Posts
Probably need to clean your coil and replace your air filters.

Is your 5hp motor single phase? Unlikely, but if so measure or replace the cap.
 
  #3  
Old 03-24-10, 06:16 AM
Member
Join Date: Mar 2010
Location: MD
Posts: 113
Received 0 Votes on 0 Posts
Overtightening the belt will cause higher amp draw and possibly premature bearing failure. Not saying this is the case.
You need to have someone check the running amps and compare it to the motor and motor starter heater setting.
You can loosen the belts a little to reduce amperage until you can have the amperage checked.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: