is it the time delay relay causing problem?


  #1  
Old 03-28-10, 09:08 AM
A
Member
Thread Starter
Join Date: Oct 2006
Posts: 77
Upvotes: 0
Received 0 Upvotes on 0 Posts
is it the time delay relay causing problem?

the fan blower keeps running even though i disconnected all connections (blue, green, white, red) to thermostat at the inside AC unit hence ruling out faulty wiring. the only power coming in to blower is the main supply.

if i disconnected the power to time delay relay (yellow coming out from the transformer), the fan stops. is the time delay relay faulty?

it is a ICM relay with four connectors numbered 3 1 2 and 5 from top to bottom. the numbers on it HBLS24A1X120, 1395-333, T1206, 24VAC

i tried looking for a similar relay but unable to find one. please help.
 
  #2  
Old 03-28-10, 01:17 PM
K
Member
Join Date: Jan 2009
Location: northeast
Posts: 78
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is the unit a furnace with A/C coil or A/C only airhandler? Could be the timer,fan relay,fan switch or high limit which would force the fan to stay on.
 
  #3  
Old 04-02-10, 07:32 PM
A
Member
Thread Starter
Join Date: Oct 2006
Posts: 77
Upvotes: 0
Received 0 Upvotes on 0 Posts
the unit was a/c only airhandler. replaced the timer delay relay. the problem disappeared. thanks for the help.
 
  #4  
Old 06-10-10, 10:33 PM
D
Member
Join Date: Jun 2010
Location: US
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
where to buy that timer delay relay?

Originally Posted by anojgoel View Post
the unit was a/c only airhandler. replaced the timer delay relay. the problem disappeared. thanks for the help.
Hi anojgoel, where could I buy that relay? since it's a discontinued item. Thanks in advance. Dave
 
 