furnace blower motor startup amps
#1
Member
Thread Starter
furnace blower motor startup amps
The service tech that comes out twice a year says that I need to replace my furnace motor. It seems to me to be working just fine.
He said that it is pulling too many amps.
I personally have two different clamp on amp meters and both read 20amps peak at startup and 7.8 amps constant.
I have a 4 speed 1/2 hp motor. The Max Amps on the furnace plate says 8.5.
I took my measurements with the furnace cover off.
Is he right or just trying to sell a new motor.
He said that it is pulling too many amps.
I personally have two different clamp on amp meters and both read 20amps peak at startup and 7.8 amps constant.
I have a 4 speed 1/2 hp motor. The Max Amps on the furnace plate says 8.5.
I took my measurements with the furnace cover off.
Is he right or just trying to sell a new motor.
#2
Member
Join Date: Dec 2005
Location: USA
Posts: 185
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The service tech that comes out twice a year says that I need to replace my furnace motor. It seems to me to be working just fine.
He said that it is pulling too many amps.
I personally have two different clamp on amp meters and both read 20amps peak at startup and 7.8 amps constant.
I have a 4 speed 1/2 hp motor. The Max Amps on the furnace plate says 8.5.
I took my measurements with the furnace cover off.
Is he right or just trying to sell a new motor.
He said that it is pulling too many amps.
I personally have two different clamp on amp meters and both read 20amps peak at startup and 7.8 amps constant.
I have a 4 speed 1/2 hp motor. The Max Amps on the furnace plate says 8.5.
I took my measurements with the furnace cover off.
Is he right or just trying to sell a new motor.
The Later. A motor works until it doesn't unless its very slow starting or very noisy. Checking a motor with the cover off is not totally accurate but I don't buy it. You need another Co. IMO. Most contract visits are just opportunities to sell you something.