a/c line is hot...

my outside a/c line running to the compressor is hot and my unit is running more than normal plus is having trouble cooling the house. thanks for any help.
 
Sponsored Links
  #2  
Old 06-23-10, 10:21 AM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 10,124
Received 34 Votes on 32 Posts
The liquid line going to the house being hot is a sign of either a dirty outdoor unit coil or the outdoor fan not turning.

Turn off the breaker to the unit and wash the coil with a garden hose.
You may see black water running from the bottom of the coil when you first do it, a sign of a plugged coil.
 
  #3  
Old 06-25-10, 10:09 AM
M
Member
Thread Starter
Join Date: Feb 2004
Location: united states of america
Posts: 81
Received 0 Votes on 0 Posts
thanks, i'll give that a try.
 
  #4  
Old 06-26-10, 02:25 AM
S
Member
Join Date: May 2009
Posts: 126
Received 0 Votes on 0 Posts
Being low on freon could also be a culprit, which would indicate a leak in the system.
 
  #5  
Old 07-07-10, 10:12 AM
M
Member
Thread Starter
Join Date: Feb 2004
Location: united states of america
Posts: 81
Received 0 Votes on 0 Posts
okay, i cleaned the outside coils but the line is still running too hot to the touch. besides low freon is there anything else i should check? also, the outside fan is working fine.
 
  #6  
Old 07-07-10, 04:19 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,484
Received 0 Votes on 0 Posts
How about your suction line (the big one) ?
 
  #7  
Old 07-08-10, 10:06 AM
M
Member
Thread Starter
Join Date: Feb 2004
Location: united states of america
Posts: 81
Received 0 Votes on 0 Posts
what should i be looking for on the suction line?
 
  #8  
Old 07-08-10, 10:42 AM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,484
Received 0 Votes on 0 Posts
Is the suction line cold/warm/hot ? or sweating ? and also, is the discharging air from your condenser hot ?
 

Last edited by clocert; 07-08-10 at 12:18 PM.
  #9  
Old 07-13-10, 03:04 PM
M
Member
Thread Starter
Join Date: Feb 2004
Location: united states of america
Posts: 81
Received 0 Votes on 0 Posts
suction line is sweating but it only feels cool not cold and yes the air being discharged is hot.
 
  #10  
Old 07-13-10, 04:55 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,484
Received 0 Votes on 0 Posts
Something is wrong here, if the discharge air is hot, the small line should not be that hot, if the small line is not cold, only cool, it should not have condensation (sweating) water. So when you touch it by hand, does it feel like ice water , or regular hose water ? Also you said the small line is hot, but how hot ? can you touch the line with you hand ? or just a little warm ? (I used to go over my neighbor's unit and touch the lines and compare. of couse you need to know their AC is in good condition, so you won't compare to a bad one). I am thinking that your big line may be not cold enough, and small line is a little too hot. All you need is to put a little more freon into the system(may be there is a small leak) . but In order to do that, you need to call an AC tech, once he is there, he can put the gauge on the system to find out more details. (another question, what is the temperature split inside house between cold vent air and return air? you want minimum 15 degrees)
 
  #11  
Old 07-13-10, 11:25 PM
C
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,484
Received 0 Votes on 0 Posts
My previous post had a typo on the first line. should say if the big line is not cold (not the small line not cold). Sorry ...
 
  #12  
Old 07-14-10, 08:36 AM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 715
Received 0 Votes on 0 Posts
Originally Posted by mfrancle View Post
my outside a/c line running to the compressor is hot and my unit is running more than normal plus is having trouble cooling the house. thanks for any help.
If there is a cottonwood tree within blowing distance of the condenser, it could be plugged with that blowing cotton.

This is a typical problem...
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: