Carrier A/C - Compressor running but not pumping
Hi all,
I have a Carrier Heat Pump (3 ton), which is about 11 years old.
The A/C worked fine until yesterday when no cold air was coming out from the vents. It is blowing mostly warm air.
The A/C seems to run fine, outdoor fan runs, and the compressor seems to run fine as well.
But the compressor is not pumping cold air...
Is there any way to repair such problems without going to the extreme of replacing the compressor? Money is very tight these days... I would appreciate your answers.
Thanks!
I have a Carrier Heat Pump (3 ton), which is about 11 years old.
The A/C worked fine until yesterday when no cold air was coming out from the vents. It is blowing mostly warm air.
The A/C seems to run fine, outdoor fan runs, and the compressor seems to run fine as well.
But the compressor is not pumping cold air...
Is there any way to repair such problems without going to the extreme of replacing the compressor? Money is very tight these days... I would appreciate your answers.
Thanks!
#2
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,340
Received 0 Votes
on
0 Posts
More info required. Is the indoor fan running?
#4
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,340
Received 0 Votes
on
0 Posts
Put your hand on the liquid line (the small one) and the vapor line (the larger one) to the compressor unit. Tell us the relative temperature.
#5
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 6
Received 0 Votes
on
0 Posts
BUT now the outside unit is not working!
The outdoor fan is not running and the compressor is not running. The unit simply makes a low mechanical buzzing/humming sound.
I felt the liquid line and it is normal outdoor temperature.
The vapor line was a little cool (only cooler compared to the liquid line).
Any ideas what happened with my AC?
Thanks.
#6
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,340
Received 0 Votes
on
0 Posts
First, check that you have 24V to the solenoid terminals of the contactor in the compressor unit. If that checks out, then...
Carefully, with a voltmeter, make sure you are getting 240V on the load side of the compressor contactor. If so, then I would suspect the capacitor.
If you aren't getting 240V on the load side of the contactor, see if you have 240V at the line side of the contactor. If so, that indicates a bad contactor.
#7
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 6
Received 0 Votes
on
0 Posts
Is the indoor fan still running?
First, check that you have 24V to the solenoid terminals of the contactor in the compressor unit. If that checks out, then...
Carefully, with a voltmeter, make sure you are getting 240V on the load side of the compressor contactor. If so, then I would suspect the capacitor.
If you aren't getting 240V on the load side of the contactor, see if you have 240V at the line side of the contactor. If so, that indicates a bad contactor.
First, check that you have 24V to the solenoid terminals of the contactor in the compressor unit. If that checks out, then...
Carefully, with a voltmeter, make sure you are getting 240V on the load side of the compressor contactor. If so, then I would suspect the capacitor.
If you aren't getting 240V on the load side of the contactor, see if you have 240V at the line side of the contactor. If so, that indicates a bad contactor.
Same sound as when it was running normally.
I don't have the tools to check for voltage... so I guess I would need to call a technician.
What would you say is a fair price for
- replacing a capacitor and
- replacing a contactor
Thanks!
#8
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,340
Received 0 Votes
on
0 Posts
But the hooker is that there seems to have been another problem before your compressor totally conked out this morning, right?
#9
Member
Join Date: Feb 2010
Location: usa
Posts: 616
Received 0 Votes
on
0 Posts
i think your compressor is shot...short to ground. and im guessing that your condenser is plugged up with dirt in the liquid line filter. either that or perhaps the compressor is running backwards? are any of your circuit breakers popped?
#10
Member
Join Date: Jul 2010
Location: canada
Posts: 1
Received 0 Votes
on
0 Posts
im in the same position can anyone help
had a tec look at my machine about a month ago and he said it was workin properly but now as the temp has risen outside my house isnt coolin down.
can any one help thanks
had a tec look at my machine about a month ago and he said it was workin properly but now as the temp has risen outside my house isnt coolin down.
can any one help thanks
#12
Could it have lost its Freon charge?
Yes, the indoor fan is running because I can hear the sound.
Same sound as when it was running normally.
I don't have the tools to check for voltage... so I guess I would need to call a technician.
What would you say is a fair price for
- replacing a capacitor and
- replacing a contactor
Thanks!
Same sound as when it was running normally.
I don't have the tools to check for voltage... so I guess I would need to call a technician.
What would you say is a fair price for
- replacing a capacitor and
- replacing a contactor
Thanks!
Could it have lost its Freon charge?
That would open a low pressure switch.
#13
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 6
Received 0 Votes
on
0 Posts
Update:
I called a technician today to look at the AC.
The first problem, which was very simple, was that the capacitor had died. So he replaced the capacitor and the AC runs.
The second problem is still unsolved.
Even after replacing the capacitor, the AC did not blow cold air.
So he checked for freon and said there was plenty.
He checked for a variety of things but in the end he could not find what the problem was.
Everything was running in the AC...
He showed me the pressure measurement.
The blue-colored one was measuring too high when he said it should measure around 70, but it is getting over 200-ish.
The red-colored one was measuring too low when he said it should measure around 250, but it is getting only 60-ish.
He said the readings are reversed but did not know why.
He said there's a strong possibility that the compressor is the problem but not guaranteed.
So I am still left with a bad AC in this summer heat...
Any advice for me?
I called a technician today to look at the AC.
The first problem, which was very simple, was that the capacitor had died. So he replaced the capacitor and the AC runs.
The second problem is still unsolved.
Even after replacing the capacitor, the AC did not blow cold air.
So he checked for freon and said there was plenty.
He checked for a variety of things but in the end he could not find what the problem was.
Everything was running in the AC...
He showed me the pressure measurement.
The blue-colored one was measuring too high when he said it should measure around 70, but it is getting over 200-ish.
The red-colored one was measuring too low when he said it should measure around 250, but it is getting only 60-ish.
He said the readings are reversed but did not know why.
He said there's a strong possibility that the compressor is the problem but not guaranteed.
So I am still left with a bad AC in this summer heat...
Any advice for me?
#14
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 6
Received 0 Votes
on
0 Posts
EDIT:
I wrote it down on paper and below is the correct measurement.
The blue-colored one was measuring 150-ish. (high pressure)
The red-colored one was measuring 120-ish. (low pressure)
I wrote it down on paper and below is the correct measurement.
The blue-colored one was measuring 150-ish. (high pressure)
The red-colored one was measuring 120-ish. (low pressure)