I am installing 8" ducting thu-out and would like to reduce to
6" at the registers, what effect will it have on volume and cfm? This is for heat only and I am maxed out on number of registers and am borderline on recommended cfm.
 
  #2  
Old 07-19-10, 07:26 PM
HVAC RETIRED's Avatar
Member
Join Date: May 2008
Location: Wisconsin USA
Posts: 713
Received 0 Votes on 0 Posts
Arrow Register's 'Ak' is in sq.ft., times the measured velocity in FPM = CFM

Originally Posted by randm View Post
1) I am installing 8" ducting thu-out and would like to reduce to 6" at the registers, what effect will it have on volume and cfm?

2) This is for heat only and I am maxed out on number of registers and am borderline on recommended cfm.
1) You need to perform a Manual D to know how the air handler & duct system will function.

The reducer from 8" to 6" will increase the velocity with a small loss in delivered CFM.

Then you will need to select diffusers that will have the desired velocity, throw & delivered CFM.

Search Hart&Cooley & Lima for register info., the 'Ak' is the free air area of the register in sq.ft., times the "measured velocity" in FPM = CFM.
 
 