did they give me the right compressor?

I have a AC wall unit. They took out a compressor that has a 25.0/10.0 MFD and put a new one in half the size that is a 25/7.5 MFD. The guy said it was the right one cause it's 10% give or take. Is he right? Was this the right one to put in? My AC wall unit does not feel as cool.
 
  #2  
Old 07-21-10, 08:17 AM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 19,281
Received 6 Upvotes on 6 Posts
I'm not positive about whether it will be ok or not...but what he is saying doesn't match what he did. Ok, the 25 is fine...but 7.5 (+ or - .75 = 8.25 or 6.75) is not w/i 10% of a 10 (11 or 9).

By the way...I think you mean capacitor...not compressor. Though if they really did replace the compressor (probably a black can about the size of a cantalope)..it might require a different cap.

Could you clarify what was actually done and why?
 
  #3  
Old 07-21-10, 08:19 AM
M
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes on 0 Posts
They replaced the compressor or the capacitor, or both? Compressors are rated by tons or Btu/hr. Caps are rated in uF.

7.5 uF is not within 10% of 10uF.
 
  #4  
Old 07-21-10, 04:15 PM
E
Member
Join Date: Feb 2010
Location: usa
Posts: 564
Upvotes: 0
Received 0 Upvotes on 0 Posts
if they just replace the capacitor then even if it is a different size it wouldnt matter cuz all the capacitor does is start the compressor. once its going the capacitor becomes unused and would have zero effect on your cooling.
 
  #5  
Old 07-21-10, 05:28 PM
M
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by ender2272
even if it is a different size it wouldnt matter cuz all the capacitor does is start the compressor. once its going the capacitor becomes unused.
Not exactly correct. Many such motors have separate start and run caps. The run cap is connected continuously.

And, PSC motors, typically used for condenser fans, have one cap for both start and run that is connected continuously.
 
 