Ac condenser fan not working


  #1  
Old 09-09-10, 01:10 PM
B
Member
Thread Starter
Join Date: Sep 2006
Location: Canada
Posts: 58
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ac condenser fan not working

30-5uf 370v capacitor, 27uf and 4.97uf tested. Compressor comes on but condensor fan does not. 1.5a on wiring to fan motor. Anything else I can do to confirm the motor is the problem. Tested 240v across both sides of contactor.
 
  #2  
Old 09-09-10, 02:49 PM
M
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes on 0 Posts
Will the fan start if you manually spin it?

Checking the capacitance doesn't prove the fan cap is OK. Most cap meters use a low voltage - the caps can leak at full line voltage.
 
  #3  
Old 09-09-10, 03:19 PM
B
Member
Thread Starter
Join Date: Sep 2006
Location: Canada
Posts: 58
Upvotes: 0
Received 0 Upvotes on 0 Posts
I checked if there was resistance with the fan blades but did not try spinning to start. not much resistance
 
  #4  
Old 09-09-10, 03:43 PM
M
Member
Join Date: Sep 2009
Location: U.S. Midwest
Posts: 1,173
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Broods
did not try spinning to start.
Try it and report back here.
 
 