Heat pump compressor only buzzes for a second at startup

Reply

  #1  
Old 05-30-11, 05:54 PM
Member
Thread Starter
Join Date: May 2011
Location: usa
Posts: 3
Heat pump compressor only buzzes for a second at startup

The system was checked out and a leak was repaired last week, all was working well until today... went out to check outer unit and hear compressor try to start. a short buzzing sound could be heard during this time for about a second... Could this be the start capacitor?
 
Sponsored Links
  #2  
Old 05-30-11, 07:14 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,245
possibly .............. does the unit run?
 
  #3  
Old 05-31-11, 03:11 AM
Member
Thread Starter
Join Date: May 2011
Location: usa
Posts: 3
Yes the blower and outside fan runs but not the compressor
 
  #4  
Old 05-31-11, 04:01 AM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,245
I would start by checking the capacitor
 
  #5  
Old 05-31-11, 03:09 PM
Member
Thread Starter
Join Date: May 2011
Location: usa
Posts: 3
Had the service company back today they found a bad connection at the compressor inside the weather head. Capacitor checked out ok.
 