Trane unit humming but not running

I need help with Trane XE 1200. The unit stopped running on the hottest day of the year, it is making a humming sound and every 30 seconds makes a louder hum for a few more seconds, as if its trying to start.

Also, I noticed that the contactors have what appears to be burn from electrical flash all around each contact

No tech can look at it for 2 days, please help
 
  #2  
Old 05-31-11, 08:03 AM
J
Member
Join Date: Oct 2005
Location: USA
Posts: 1,017
Upvotes: 0
Received 0 Upvotes on 0 Posts
Could be a bad capacitor.
 
  #3  
Old 05-31-11, 08:10 AM
D
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks, i'll give that a try
 
  #4  
Old 05-31-11, 03:57 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
most likely bad capacitor or hard start. IF contacts look that bad, then replace the contactor as a precaution..... doubtful has anything to do with current problem though.
 
  #5  
Old 05-31-11, 05:17 PM
D
Member
Thread Starter
Join Date: May 2011
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Great call guys, the air is on and running like a champ! Hard to believe I would have waited two days for a thirty minute fix, many thanks and bless you both
 