help Im melting

Hello my friend I have a Trane XE 1000. My compressor hums faintly and my contactor switch clicks in when the Therostat is switched on. But fan won't move and out of the brown ,black, red ,purple wires coming from the fan motor the red wire is not connected is this normal
 
  #2  
Old 07-18-11, 07:27 AM
R
Banned. Rule And/Or Policy Violation
Join Date: Jul 2011
Location: USA
Posts: 19
Upvotes: 0
Received 0 Upvotes on 0 Posts
What you need to do

Ok Since you weren't very clear , Heres what ya need to do . The red wire either needs to go to a silver cylinder . or it needs to go to your low voltage contactor .

The Low Voltage contactor is typically brown looking and will have a spade where the red wire should have a plug on it that will go over the spade. The same applies to the silver cylinder (Capacitor) Hope this helps it is a easy fix.

You may have 2 silver cylinders , One being for the fan , the other being for compressor .
 
  #3  
Old 07-18-11, 03:27 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 5,491
Upvotes: 0
Received 4 Upvotes on 4 Posts
NO! The red wire is low speed for the fan and was not used on all models! As said, the capacitor may be the problem, but you need to verify you have voltage on both sides of the contactor.
 
 