Central Air Outside Unit Fan Failed / Compressor Overheated / Not Working Now

Central Air Outside Unit Fan Failed / Compressor Overheated / Not Working Now

Reply

  #1  
Old 08-12-11, 05:53 PM
N
Member
Thread Starter
Join Date: Aug 2011
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
Central Air Outside Unit Fan Failed / Compressor Overheated / Not Working Now

I have an Armstrong Concept 10 unit with a Copeland 3 ton compressor. When I came home today the fan had locked up on the outside unit. I assume the compressor overheated and won't start now. Just wondering if there is something I can check or do. Is replacement of the compressor my only option?

Thanks
 
Sponsored Links
  #2  
Old 08-12-11, 06:20 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
If the fan spins freely with power removed, you may only need to replace the run capacitor.





The compressor can be cooled with a water hose to reset the thermal lockout. (turn off power first)
 
  #3  
Old 08-12-11, 06:36 PM
S
Member
Join Date: Sep 2008
Location: Long Island
Posts: 769
Received 0 Votes on 0 Posts
the compressor tripped as it should of with no condenser fan running...shhut off disconnect put a garbage bag over it an run a spray over it...or just leave off overnight to cool off.in the morning power it bak up no stat calling and take a pencil and push the contacotr in just for a second ..if compressor runs its OK...now consider as suggested new cap...was the body of the fan motor super hot.
 
  #4  
Old 08-12-11, 07:03 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
In 20 years of service I have never used a trash bag to cool a compressor. What do you cover?

The fan motor gets hot when you need a new cap.
 
  #5  
Old 08-13-11, 03:59 AM
S
Member
Join Date: Sep 2008
Location: Long Island
Posts: 769
Received 0 Votes on 0 Posts
30yrs in the field the COMPRESSOR...DAH commercial equipment get condensers washed and any and all item within range and ba booom on a restart this guy has problems already little caution ..won't make another 13 gallon bag you use for kitchen container works great... did you think i was talking about the entire condenser
 
  #6  
Old 08-13-11, 04:09 AM
N
Member
Thread Starter
Join Date: Aug 2011
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
The fan was hot when I first noticed the unit not working. The fan spins freely but I need to push it to get it to spin. Otherwise it just buzzes. When I take off the cover I see four major components. The fan, the compressor, the capacitor, and a small electrical circuit component (must be the contactor).

The contactor looks like this ...



Not sure if I should replace that as well as the capacitor. What do I push with the pencil?
 
  #7  
Old 08-13-11, 07:46 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
I'm surprised the trash bags don't melt to the compressor. Guess they are not very hot when you do this. It is not required, the compressor runs just fine in the rain, probably wouldn't hurt though


Replacing that single pole, 24 volt contactor wouldn't be a bad idea.

Push here to manually engage the contactor...
 
  #8  
Old 08-13-11, 08:12 AM
N
Member
Thread Starter
Join Date: Aug 2011
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
OK After letting it cool all night the fan still needs a push to start and the compressor doesn't start. I am going to try changing the capacitor. The contactor seems to be engaged as the fan runs after a push.

Here is a picture of the device. Armstrong SCU10B36A-3, Copeland CR34KF-PFV-130

Haven't taken the capacitor off yet to get the specs. Hopefully I can find somebody local who carries the parts.

 
  #9  
Old 08-13-11, 08:27 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 7,426
Received 17 Votes on 14 Posts
I would not buy a contactor before proving that the compressor will run.
I hope the cap values are not written on the rusty part of that dual capacitor.
The top of the compressor and the fan motor may also display capacitor requirements.

Sears has a $30 meter that can measure caps.





You should read plus or minus 6% of the listed value. (10% is listed on some caps)
 
  #10  
Old 08-13-11, 12:34 PM
N
Member
Thread Starter
Join Date: Aug 2011
Location: United States
Posts: 4
Received 0 Votes on 0 Posts
Smile

I went ahead and bought a new capacitor for $40 at a local parts dealer. Just put it in. Everything is working great! Thank you so much for your replies! Greatly appreciated.
 
  #11  
Old 09-03-12, 03:49 PM
H
Member
Join Date: Sep 2012
Posts: 1
Received 0 Votes on 0 Posts
Mind sharing the microfarad rating on the capacitor? I cannot find it anywhere. The old cap is completely rusted, and the manual only says to check the side of the old cap, go figure. I have the exact same compressor (cr34kf-pfv-130). Many thanks.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: