Identify Part
#1
Member
Thread Starter
Join Date: Jun 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Identify Part
I have a Carrier central air/heating unit. The breaker was thrown this morning when I get up. I turned the breaker on, the inside unit worked as normal. After 15 minutes or so, I noticed the air being blown out was pretty much room temperature, and that the unit outside was not working. The fan outside was not froze up. After a little more investigation, I found this on the outside unit:

It was still a little warm, and smelt like someone was welding.
Can anyone identify what part this is, confirm that it is most likely why the outside fan is not working, and advise how I should proceed?
Thanks in advance.

It was still a little warm, and smelt like someone was welding.

Can anyone identify what part this is, confirm that it is most likely why the outside fan is not working, and advise how I should proceed?
Thanks in advance.
#3
Looks like blown terminals on the compressor.
Unless it is still under warranty, I'm confident that you need a new outdoor unit.
If the unit is at 0psi or the (isolated) compressor measures continuity to ground, you definitely need a new unit.
You have about a 5% chance that it is only the wiring at the compressor. If this is the case I recommend the Qwik Lug repair kit for this problem...

QT2810-QT2812-QT2910-QT2912 QwikLug
Unless it is still under warranty, I'm confident that you need a new outdoor unit.
If the unit is at 0psi or the (isolated) compressor measures continuity to ground, you definitely need a new unit.
You have about a 5% chance that it is only the wiring at the compressor. If this is the case I recommend the Qwik Lug repair kit for this problem...

QT2810-QT2812-QT2910-QT2912 QwikLug
Last edited by Houston204; 06-30-12 at 11:41 AM.
#4
Member
Thread Starter
Join Date: Jun 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you Houston204 and guyold for the responses. To clarify, there is high chance that the unit is junk. Does this most likely mean the compressor unit only needs replaced, or the entire unit outside (fan, housing, compressor, etc)?
#5
If it is a grounded compressor...
Under warranty, replace the compressor.
Not under warranty, replace the entire outdoor unit.
Do you own a meter?
Under warranty, replace the compressor.
Not under warranty, replace the entire outdoor unit.
Do you own a meter?
#7
Turn off the breaker, write down the wire color = terminal arrangement that your compressor is using, remove the 3 wires, set the meter for ohms, check each compressor terminal to ground.
Any reading other than infinity (OL) to ground would indicate a grounded compressor.
Carrier usually uses this terminal arrangement...
Common / Start
Run
Wear safety glasses
Refrigerant and oil is 150 to 200 psi here when the unit is off and the terminals are damaged
Any reading other than infinity (OL) to ground would indicate a grounded compressor.
Carrier usually uses this terminal arrangement...
Common / Start
Run




#9
Member
Thread Starter
Join Date: Jun 2012
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you both again for the quick responses.
I didn't make it as far as testing the ground. I pulled the plug off and one of the terminals crumbled. The inside of the plug too looked impressive.
I am not sure how old the unit is. The model number on the outside unit is "38YMA036320". I think its time to start calling around for quotes on a new system as suggested. Should I expect them to recommend replacing the inside unit as well (because of the age, or is it likely a newer outdoor unit is incompatible with what I have on the inside)?
I didn't make it as far as testing the ground. I pulled the plug off and one of the terminals crumbled. The inside of the plug too looked impressive.
I am not sure how old the unit is. The model number on the outside unit is "38YMA036320". I think its time to start calling around for quotes on a new system as suggested. Should I expect them to recommend replacing the inside unit as well (because of the age, or is it likely a newer outdoor unit is incompatible with what I have on the inside)?

#11
The first digits of the serial number indicate week and year of manufacture.
I recommend replacing the air handler as well with heat pumps since the indoor coils serves as the condenser coil in the heat mode.
I recommend replacing the air handler as well with heat pumps since the indoor coils serves as the condenser coil in the heat mode.