Carrier Outside Unit does not run, inside does, no power to outside unit
Old 06-30-12, 11:45 AM
My Carrier system inside unit runs and blows air. No error codes from the light
The outside unit makes no noise and does not turn on.
I flipped the inside breaker off/on, no change.
I used my voltmeter and pulled the disconnect on the outside wall mounted box and checked both line and load voltages...I got nothing on either.
Is this purely a AC power to the outside unit issue? There was no fuse in the outside disconnect, but from my measurement, it wasnt getting any power anyway.
Does the inside unit control if the outside gets power?
Advice appreciated. It is 106 here!!
Old 06-30-12, 12:00 PM
Houston204's Avatar
Received 94 Upvotes on 87 Posts
Does the run capacitor appear swollen on top like this one?
Old 06-30-12, 12:06 PM
I will check the capacitor.
However, I just pulled the cover to check the contactor. My multi-meter was on 'auto' which apparently doesnt work...as I changed the range, I got 240V to BOTH sides of the contactor and 24v on the low voltage sides. So that appears OK. (the unit is asking for cool inside)
Does this point to a motor or is there still a relay or something that could be bad?
What does the above capacitor do?
thx
Old 06-30-12, 12:24 PM
Here are pictures of the capacitor
Size:  32.0 KBName:  IMG_5503_small.jpg
Size:  43.0 KBName:  IMG_5504_small.jpg
Old 06-30-12, 04:09 PM
hvactechfw's Avatar
Received 4 Upvotes on 4 Posts
yep its swollen on top. replace it.
Old 06-30-12, 05:44 PM
thanks. I ordered one. I will look locally on Monday but ordered one just in case.