Circuit breaker issue - walkin cooler
#1
Member
Thread Starter
Join Date: May 2012
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Circuit breaker issue - walkin cooler
have a walkin refrigerator and the circuit breaker relating to the evaporator/fan trips occassionally. separate compressor circuit breaker does not trip.
the compressor is located in a poorly overheated area on top of cooler
is there a chance that the evaporator/fan circuit breaker is shutting down due to excessive heat generated by the compressor?? i.e to protect the compressor? what would cause the circuit breaker to trip (amp capacity on circuit breaker is fine)
(ie. area where compressor is located gets as hot as 115 degrees continually due to no ventilation) - manuf says temp should be under 90.
thanks
the compressor is located in a poorly overheated area on top of cooler
is there a chance that the evaporator/fan circuit breaker is shutting down due to excessive heat generated by the compressor?? i.e to protect the compressor? what would cause the circuit breaker to trip (amp capacity on circuit breaker is fine)
(ie. area where compressor is located gets as hot as 115 degrees continually due to no ventilation) - manuf says temp should be under 90.
thanks
#2
The circuit breaker is there to protect the circuit wiring. The motor should be protected by some other protection like internal thermal protection or fuses. Heat dose not normally cause a breaker to trip unless the breaker itself is subjected to the high heat. You said the amp capacity is fine but you do not give a number.
What is the amp rating of the breaker and how many amps are being drawn? (Take a reading with a clamp on meter) Is the a single phase or three phase motor/cooler?
What is the amp rating of the breaker and how many amps are being drawn? (Take a reading with a clamp on meter) Is the a single phase or three phase motor/cooler?
#4
Member
Thread Starter
Join Date: May 2012
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
evaporator/fan - fuse problem
thanks
the evaporator/fan circuit is separate from the compressor circuit
if the evap fins are dirty (havent been cleaned for yrs) would this cause fan to draw more amps and then cause breaker to trip?
it is a 20 amp breaker (has been replaced so the breaker is likely OK) and the evap/fan is 1 phase (115 v) and a 1/15 HP motor so the breaker seems plenty big enough
the evaporator/fan circuit is separate from the compressor circuit
if the evap fins are dirty (havent been cleaned for yrs) would this cause fan to draw more amps and then cause breaker to trip?
it is a 20 amp breaker (has been replaced so the breaker is likely OK) and the evap/fan is 1 phase (115 v) and a 1/15 HP motor so the breaker seems plenty big enough
#9
Member
Thread Starter
Join Date: May 2012
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
electr diag for evaporator and compressor
included in post above is the electrical schematic for the evaporator (on right) - appears the temp control is line voltage
i see the temp probe sticking out from the wall of unit on the inside
how/why would thermostat control be getting wet? thanks
i see the temp probe sticking out from the wall of unit on the inside
how/why would thermostat control be getting wet? thanks