changed contactor on a/c unit and still wont turn on
#1
Member
Thread Starter
Join Date: Aug 2012
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
changed contactor on a/c unit and still wont turn on
I will rephrase from subject line i can manually push the button and the condenser and fan will turn on but not by t-stat i changed the other contactor because it looked like it was burnt on the pole post's .
But it all happened this morning i was already at work and my wife said the the air conditioner was fine, i got home early from work and she turned the t-stat down cause we were going to w-mart. when we got back the blower was on but it wasnt getting cool so we checked outside unit and it wasnt on. i pushed the old contactor button and it turned on so naturally i thought it was the contactor being bad and not staing down. Nope i bought a new one and still no pulling down of the contactor button.
Please help whole unit wors and cools down just not until you manually push down the contactor button .
is it possibly the capasitor ?
thanks in advanced
But it all happened this morning i was already at work and my wife said the the air conditioner was fine, i got home early from work and she turned the t-stat down cause we were going to w-mart. when we got back the blower was on but it wasnt getting cool so we checked outside unit and it wasnt on. i pushed the old contactor button and it turned on so naturally i thought it was the contactor being bad and not staing down. Nope i bought a new one and still no pulling down of the contactor button.
Please help whole unit wors and cools down just not until you manually push down the contactor button .
is it possibly the capasitor ?
thanks in advanced
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
First thing to do is check for 24 volts (more or less) at the contactor coil terminals after a five minute delay from the thermostat calling for cooling. If no power then check the low voltage wiring from the furnace (air handler) to the condensing (outside) unit.
#6
Member
Thread Starter
Join Date: Aug 2012
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
yes i have a circuit board on the outside unit which sends the contactor the pull and push i beleive right now i need to figure out where to get it
should the a/c place where i got the contactor probably has it correct
should the a/c place where i got the contactor probably has it correct
#7
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I'm more inclined to think your unit has a terminal board, not a circuit board. Merely a place to terminate all the wiring.
The contactor does not receive a "pull and push" but a 24 volt AC signal to the coil of a solenoid. When the coil is energized the contactor closes the high voltage (240 volts AC) to the compressor and the cooling fan motor. When the 24 volt signal is off a spring opens the contacts on the high voltage turning everything off.
Post a few pictures of your contactor and this "circuit board" and we can better help you.
...which sends the contactor the pull and push i beleive...
Post a few pictures of your contactor and this "circuit board" and we can better help you.
#8
Member
Thread Starter
Join Date: Aug 2012
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
[HR][/HR]it is the board where the t-stat wires hook up to then a bunch of lettering's on below where other wires hook up like t-1 and t-2
but when i get home from work i will post some pics
also let me say something when the unit is turned on by tstat
the contactor button clicks then bounces like it wants to pull down but just cant
but when i get home from work i will post some pics
also let me say something when the unit is turned on by tstat
the contactor button clicks then bounces like it wants to pull down but just cant
#12
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
Yep, that's a circuit board. Sorry for doubting what you wrote.
With the power off (pull the local disconnect switch) you need to carefully move the wires around and look on the contactor for the "coil volts) numbers. Most common is 24 volts AC but the wiring on the coil terminal visible (the terminal on the right side with the black wire) leads me to believe it could be a 240 volt coil. Check this black lead and also the one on the terminal on the left side (obscured in the picture by the wiring bundle) carefully for breaks, especially where it is connected to the push-on terminals of the contactor and also at the circuit board.
Look carefully at the low-voltage wiring coming from the house to the unit. It appears to connect to the circuit board on the lower left side.
With the power off (pull the local disconnect switch) you need to carefully move the wires around and look on the contactor for the "coil volts) numbers. Most common is 24 volts AC but the wiring on the coil terminal visible (the terminal on the right side with the black wire) leads me to believe it could be a 240 volt coil. Check this black lead and also the one on the terminal on the left side (obscured in the picture by the wiring bundle) carefully for breaks, especially where it is connected to the push-on terminals of the contactor and also at the circuit board.
Look carefully at the low-voltage wiring coming from the house to the unit. It appears to connect to the circuit board on the lower left side.
#13
Member
Thread Starter
Join Date: Aug 2012
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
nah no worries on the doubt pictures are thousand words so i put em
now so you dont think its the board or capacitor because the contactor is new
so does the 2 side prongs that come from the board give the ok to the contactor to tell the fan condensor to work
the tstat turns on the blower in the house just not the outside so its possibly not the board cause thats bout 155-200 dollars
now so you dont think its the board or capacitor because the contactor is new
so does the 2 side prongs that come from the board give the ok to the contactor to tell the fan condensor to work
the tstat turns on the blower in the house just not the outside so its possibly not the board cause thats bout 155-200 dollars
#14
Member
Join Date: Feb 2010
Location: usa
Posts: 564
Upvotes: 0
Received 0 Upvotes
on
0 Posts
yeah jump y and c from the circuit board, where the wires come into the board, and attach them to each side(left/right) of the contactor where 24V goes. But do note, that this will only fix the ac and not the heat.
#19
Member
Thread Starter
Join Date: Aug 2012
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
i got ya thats cool for now i will use the jumper untill i can get the board i seen a site or i will try my local a/c shop see if they can get it for cheaper then $155
i appreciate this very much you helping me out i am pretty savvy but not a/c savvy
thank you
i appreciate this very much you helping me out i am pretty savvy but not a/c savvy
thank you
#21
Member
Join Date: Oct 2010
Location: USA
Posts: 163
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I suggest you try cleaning all those corroded connections to the circuit board before buying a new board. Reseat connectors and you could spray them with a contact cleaner. I use DeOxit but it is over priced. You could check the circuit board for cold solder joints. They can go bad from excessive heat and/or vibration. Reflow any that look bad if you know how to solder, I would not touch them if you don't know how. You need to use a low power iron with small boards like these.