What should the split temps be inside and outside?
Old 10-13-12, 09:08 AM
B
I realize it may vary and the larger the split the better, but is there a ballpark figure minimum for the desired split difference for the inside and outside? Are they suppose to match almost?
Thank you.
Old 10-14-12, 06:50 AM
hvactechfw's Avatar
Received 4 Upvotes on 4 Posts
split between supply and return inside should be 15-20F
Old 10-19-12, 05:48 AM
HVAC RETIRED's Avatar
You size cooling equipment by the split between outdoor & indoor temps & the indoor humidity load & the summer design for your climate area.
Additionally, a room by room heat-gain calc needs to be performed to determine equipment & duct system design & sizing.
The indoor design target is normally 75-F & 50% or less relative humidity; the outdoor design temp will determine the sensible split; 90-F outdoors 75-F indoors is a 15-F sensible split, etc.
At 50% relative humidity, with tight ductwork, the indoor split at an airflow 400-CFM should normally be 19 to 21-F; higher humidity levels will result in lower indoor SA/RA temp-splits & higher condenser temp-splits compared to outdoor temps.