gas furnace blower won't turn on
the blower on my furnace wont turn on im getting a pressure sw stuck open message the blower motor is buzzing but not turning i tried spinning it with a nail about 15 times it started once for about 10sec then stopped. 1997 rheem gas furnace .
#2
If you're getting a pressure switch open code then that must be the draft inducer blower you are having issues with.
On a call for heat....that blower must be up to normal speed or you'll get that code and no ignition.
Looks like it's time for a replacement.