Is smaller copper line COLD and Sweat during the COOL cycle?

Situation: Just rent a vacant office space. AC not working for who knows when, but had AC expert looked through and he replaced New outside unit fan motor, recharged R22 (5lbs). System ran nicely with cold cold air (65F measured at vent). But then felt no cold air blowing out of vent any more after 2, 3 hrs and of course, after the AC tech went away. Found A/H blower unit fan quit. Small copper line froze from air handler to the compressor.

I replaced A/H blower motor, system is now running, but no longer gives out cold air. Noticed that smaller copper line is cold and sweating. Something wrong here?
Thanks.
 
Sponsored Links
  #2  
Old 02-12-13, 03:51 PM
hvactechfw's Avatar
Member
Join Date: Jan 2011
Posts: 6,245
Received 0 Votes on 0 Posts
Sounds like it is low on charge or a metering device issue. These are NOT DIY problems to try and fix, call the pro back.
 
  #3  
Old 02-13-13, 06:46 AM
Member
Thread Starter
Join Date: Feb 2013
Location: usa
Posts: 2
Received 0 Votes on 0 Posts
Thanks my friend. I hear you. Here is also the picture of the indoor coil. http://img841.imageshack.us/img841/9730/img3944n.jpg
 
  #4  
Old 02-13-13, 07:14 AM
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,459
Received 0 Votes on 0 Posts
Frozen line may indicate low Freon, cold and sweat copper line is a good sign, but don't know why you don't get cold air. can be blocked coil, or.... This is not a DIY site if any work related to Freon charges, you can go to other diy forum for more details or call a pro.
 

Last edited by clocert; 02-13-13 at 07:16 AM. Reason: typo
  #5  
Old 02-13-13, 12:47 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,916
Received 24 Votes on 19 Posts
The smaller, uninsulated line should never be cold in cooling mode, let alone have condensation. (normally it should be well above the outdoor temperature)

There's most likely a major restriction in the outdoor unit itself. (plugged filter drier or otherwise)

Many problems can be misdiagnosed as a refrigerant leak if the tech doesn't know what he's doing.
 
  #6  
Old 02-14-13, 05:10 AM
Member
Join Date: Feb 2013
Location: India
Posts: 1
Received 0 Votes on 0 Posts
Check your TXV.

99% it'll be blocked or the suction line.
 
  #7  
Old 02-14-13, 07:45 AM
Member
Join Date: Aug 2008
Location: Texas, California
Posts: 1,459
Received 0 Votes on 0 Posts
Sorry, I was wrong, the small copper line should never be cold, Muggle is right. I do not know why I said that, age must got into me....
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: