checking compressor


  #1  
Old 04-26-13, 02:27 PM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
checking compressor

What are the steps needed to take to test compressor and windings ,w meter ,and voltage to it/ohms ,etc ?I dont believe its good but want to check it out before concluding replacement.
any info is appreciated
 
  #2  
Old 04-26-13, 05:02 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
The compressor terminals can discharge high pressure refrigerant and oil into your eyes if they are damaged. I recommend Wearing Safety Glasses.

Remove power to the outdoor unit at the service disconnect or breaker (not from the thermostat)

Wait a few minutes for the capacitors to bleed down.

Take a picture or write down the color of wires at each compressor terminal.

If the terminals look like this you have a bad compressor...


Isolate (unwire) the compressor and measure for continuity between each terminal to ground with a meter that can measure millions of Ohms. (Should read Infinity)

Measure Common to Start, Common to Run, and Start to Run...



If the compressor checks out ok with those tests, wire it in again and restore power.

Measure the starting amperage and running amperage of the compressor and compare to the RLA and LRA rating on the unit nomenclature.
 
  #3  
Old 04-27-13, 07:44 AM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
Those most common cause for a compressor not to run is a weak or swollen capacitor...



Capacitors should not appear swollen on top...
 
  #4  
Old 04-27-13, 10:10 AM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
Has new capacitor old one tested ok but wanted to start fresh and contactor is working fine .
Thanks for info ,im thinking the windings/compressor but will still need to test s,c and r..
Also what is the correct voltage reading /settings going to compressor , off contactor and capacitor where it plus into compressor?
 
  #5  
Old 04-27-13, 01:14 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
Are you asking me if you have a 240 volt AC unit?
Probably, but you should refer to the unit nomenclature.

What's the unit doing?

Running but not cooling?
Tripping the breaker?
Cooling but sounds terrible?
Will not start?
 
  #6  
Old 04-27-13, 07:57 PM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
compressor is not coming on
 
  #7  
Old 04-27-13, 08:19 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,418
Received 74 Upvotes on 67 Posts
Does the outdoor fan motor run?
Can you hear the compressor try to start?
 
  #8  
Old 04-28-13, 12:47 AM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
Am gonna send a pic soon,noticed burn mark below the conn?ector ,is that a sign of overheating?
Yes the fan kicks in when turned on .
 
  #9  
Old 04-28-13, 01:03 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,022
Received 3,409 Upvotes on 3,059 Posts
If the condensor fan kicks on then that means your contactor and income power wiring is ok.

Burned mark on which connector ?
 
  #10  
Old 04-28-13, 08:37 AM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
The mark is on outside of compressor near lable a tad under connector cover.no burn marks at connector.here is pic.
 
Attached Images  
  #11  
Old 04-28-13, 09:27 AM
G
Member
Join Date: Nov 2011
Location: USA
Posts: 593
Upvotes: 0
Received 2 Upvotes on 2 Posts
Also scratch off some paint on compressor and see if you have a short from any pins to case when you take ohms.Would think it would throw breaker though,stranger things have happened.Good luck.
 
  #12  
Old 04-28-13, 09:55 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,022
Received 3,409 Upvotes on 3,059 Posts
I see the spot. Hard to tell exactly what happened from the pic. Looks like possibly one of the windings inside the motor shorted out there.

Now that you have the wiring cover of the compressor off you can make your measurements.
Do make sure the disconnect for that unit has been off for several minutes before disconnecting the wiring. Wouldn't hurt to short those terminals to ground before touching them.
 
  #13  
Old 04-28-13, 05:51 PM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
Thanks for the info.If all checks out ok would it be worth trying a hard start booster at capacitor sometimes called quick start,etc to energize the start up?
 
  #14  
Old 04-28-13, 11:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,022
Received 3,409 Upvotes on 3,059 Posts
Get the compressor running first. If it's not even trying to start.... a hard start booster would be a moot point.
 
  #15  
Old 04-29-13, 07:50 PM
T
Member
Thread Starter
Join Date: Nov 2012
Location: usa
Posts: 415
Upvotes: 0
Received 3 Upvotes on 3 Posts
Looking like I'll need another compressor . Nothing on any of the 3 ohms test on the compressor test even showed any readings nor ground....
 
 